suggestion for controlling vibration of DG set.

03/09/2008 7:52 AM

we have one DG set of 200 KVA,crompton make model TBD3 V6 in our company for the past two and a half year running.It is observed that it is giving mild to noticeable vibration when run on 50% load only.It is running smooth on full load. Job done to rectify are: a)tuning of governer. b) capacitors were put off the feeder line in the remaining part of load for checking. No improvement in vibration stopping.Requested valuable advice from the forum for rectification.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2007
Posts: 1790
Good Answers: 87
#1

Re: suggestion for controlling vibration of DG set.

03/09/2008 1:38 PM

Really need more info...

Have you taken in vibration data? Is it on the engine side or the generator side? What aspect or part of the machine is the vibration noticable on? It is fine on full load, bad at 50%, how is it at no load? Anything broken? Motor mounts in good shape?

Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: suggestion for controlling vibration of DG set.

03/09/2008 5:32 PM

What Vibrations are you getting??

Vibrations within the Generator Set or Vibrations through the Building Structure??

The first could be caused by Broken Mounts etc mentioned previously.

The Vibrations through the Building are quite ofter caused but Harmonics where the Genset Vibrations resonate with the building at a given point.

You need to identify what Vibrations you are getting before you get to far find you are chasing a non-existant mechanical problem.

Regards
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Commentator

Join Date: Oct 2007
Location: Caribbean
Posts: 79
Good Answers: 2
#3

Re: suggestion for controlling vibration of DG set.

03/10/2008 9:23 AM

From my experience , broken mounts or resonance are the culprit.

A 200KVA is a relatively small machine.

Verify the spped at 505 load and confirm if the governor is holding the speed the same at 100% load.

If not and you can shift the speed at 505 to match the speed at 100% this will eliminate the suspicion that it is a speed resoannce at the 50% load.

saw it happen many times .

Even saw an output terminal box with slack bolts cause a partial load resonance but that was on a 1.5MVA man B&W.

last titbit, if the machine was ruunning fine all along then even if it tis resonance , something has changed.

broken mounts , loose anchor bolts, does the machine have a "soft leg"?

__________________
Learn more, Do more , Be more
Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#4

Re: suggestion for controlling vibration of DG set.

03/11/2008 12:05 AM

Is it puffing any smoke at part load? If it is maybe a bad injector is to blame. I suggest you get the engine manufacturer to perform a PM clinic on the engine, it could save bigger expense.

Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2008
Posts: 5
#5
In reply to #4

Re: suggestion for controlling vibration of DG set.

03/11/2008 3:28 AM

Thanks for your comments.it is giving more smoke at the start only.planning to check injectors and then calibration of the injection pump.your valuable comments are welcome.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#6
In reply to #5

Re: suggestion for controlling vibration of DG set.

03/12/2008 7:42 AM

I would go with the Bad injectors,causing the vibration line of thought.

cheers

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

chaterpilar (1); djacob (1); Emjay4119 (1); MAINTENANCE@SANKAR.COM (1); Sapper (1); Steve S. (1)

Previous in Forum: electrical installations..   Next in Forum: Split phase rotation
You might be interested in: Vibration Instruments, Vibration Sensors

Advertisement