VFD related

03/25/2008 1:07 AM

what is the effect on the system if we increase the frequency of the vfd supply to motor for icreasing the speed of pump

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate
Engineering Fields - Energy Engineering - New Member India - Member - Jack of all trades

Join Date: Jan 2008
Location: India
Posts: 43
Good Answers: 2
#1

Re: VFD related

03/25/2008 2:28 AM

Not absolutely sure though, but I think, this will inject harmonics into the system.

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.
Register to Reply
Member

Join Date: Jan 2008
Posts: 8
#6
In reply to #1

Re: VFD related

03/26/2008 3:28 AM

i dont think harmoincs will inc , bcoz theris 3 core transformer which will mitigate the harmonics..it may be related with torqe and pump aur power requirement

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: VFD related

03/25/2008 2:34 AM

There will be a mechanical limitation on the motor and Pump based on the design.Second the torque starts decreasing when u run above syn . speed with Power remaining constant.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: VFD related

03/25/2008 5:15 AM

Bear in mind that for a centrifugal pump, the characteristic curves are drawn for specific impeller speeds; doubling the frequency does not produce double the flow, as the system characteristics need to be considered too. The operating point is where the pump characteristic and the system characteristic curves intersect.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: VFD related

03/25/2008 9:29 AM

Bingo. Good answer vote.

And as also said above, the power (kW or HP) and thereby the torque requirement of the load will increase (although not linearly) with the slightly higher flow, but above full rated speed the motor output power cannot increase and with a flat kW/HP, the motor torque drops off rapidly. Less torque but more load = more slip = higher current draw = eventual overload! You might get a very slightly higher flow out of your pump because although what PWSlack says is true, no pump design matches a given motor speed exactly. You might be able to take advantage of a slight "overshoot" in the design curve, but at the cost of exponentially increase motor loading which effectively shortens your motor life (if it stays running at all)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#5

Re: VFD related

03/25/2008 9:40 AM

At frequencies above the base frequency (50 or 60Hz), the motor will have to be derated. I don't have the data here at home though. It's in the office under a pile of other data that I don't need.

You also need to consider that the mechanical equipment that the motor is driving is probably not designed to run too much beyond the nominal speed. It's very possible that the pump could self-destruct if you push it too high (I wouldn't like to be standing next to it when it does).

Then there's the failure rate for bearings and seals.

When asked this question by my workmates, my answer is always "buy a higher capacity pump and the motor to match".

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

admire_azit (1); j_kamal (1); JRaef (1); nesubra (1); PWSlack (1); Vulcan (1)

Previous in Forum: Street Lights Poles   Next in Forum: Spare Transformer Along with Bank of Single Phase Transformer

Advertisement