Anonymous Poster

EHV and HV transformer size

03/27/2008 5:25 AM

Can any one tell the ratings of Power Transformes, and ICTs

(a) 400/220 kV

(b)400/220/33 kV

(c) 400/220/132 kV

(d) 220/132/11 kV

(e) 220/132/33 kV

(f) 220/132 kV

(g) 220/33 kV

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: EHV and HV transformer size

03/27/2008 6:47 AM

Not from those figures. Units of kW and MW would be needed.

Reply Score 1 for Off Topic
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2

Re: EHV and HV transformer size

03/27/2008 11:45 PM

Refer to IEC 60076 or some standard trafo manufacturer.

__________________
BNDas
Reply
Anonymous Poster
#4
In reply to #2

Re: EHV and HV transformer size

10/23/2009 4:53 AM

Standard : IEC 600076

Capacity: 100 MVA

Type of cooling : ONAF

Email: karunasarma@gmail.com

Reply
Associate
Engineering Fields - Energy Engineering - New Member India - Member - Jack of all trades

Join Date: Jan 2008
Location: India
Posts: 43
Good Answers: 2
#3

Re: EHV and HV transformer size

03/28/2008 1:22 AM

Power transformer rating is not a function of the voltage level, instead, the amount of power needed to be evacuated/transmitted shall be the determing factor for transformer rating. Which in turn, depends upon the installed capacity of generating station.

Generally, there are three levels of a power system network -

1. Transmission - Normally at EHV voltage levels

2. Subtransmission - Normally at HV/MV levels

3. Distribution - MV/LV levels

Finally, after stepping down the voltage, power supply is connected to consumer premises through cable etc in case of LV consumers, whereas for bulk consumers, power supply is given at higher voltage level(s) to consumer's grid substation.

The rating of transformers may vary from 11 KV, 25 KVA to say.. 400 KV, 500 MVA depending upon manufacturer.

As righly pointed out by Mr. B.N. Das, you can refer the IEC standard and for specific information regarding the capacities of transformers meant for various voltage levels, contact manufacturers.

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.