Motor voltage & frequency

03/30/2008 12:29 AM

Is it safe to connect a 380V, 60Hz ac motor to 415 V,50Hz ac supply. What is the effect on motor output due to it. If not safe, what is the remedy

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Motor voltage & frequency

03/30/2008 1:05 AM

Hello nambiathiri

If the motor is a squirrel cage induction motor, it will run slower, of course, at 5/6 of the nameplate speed, on the lower frequency supply.

We commonly have connected 60Hz 380v motors to 400v supply here, without any bother at all, apart from the speed difference, and our Mains Voltage varies from the nominal 400 V to 380V minimum - 420 V maximum as allowed by local Electrical Supply Regulations.

In most Electrical Supply areas, Mains Voltage range is normally +/- 5% which at 380 Volt Supply +5% is 399 Volts, and your 415 Volt supply should probably be safe to use, even though a small increase above normal nameplate voltage.

Carefully check motor current in your situation, at both No Load and Full load, should you intend using the motor on a permanent basis.

Remember that at the lower speed, there is less fan cooling on a Fan Cooled motor, and if you note the motor case getting too hot, arrange for extra cooling.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#2

Re: Motor voltage & frequency

03/31/2008 9:32 AM

dear

the reason is at 60hz the impedance of the motor matches to 380V.this is desided by the ampereturns of the coil and core maximum flux density.

the only remedy is to reduce suply voltage at 50hz.

but the power remains the same after reducing(stepdown) 415volte to apropriate value.

thanQ

RRekhapalli

Register to Reply
Associate

Join Date: Oct 2007
Posts: 43
#3

Re: Motor voltage & frequency

03/31/2008 10:21 AM

Since inductive reactance is proportional to frequency, the stator current at a given voltage will be higher at 50Hz compared to the current at 60Hz.

European standards permit 10% variation on mains supply. Thus 415 VAC is permissible for motor rated at 380VAC.

The cumulative effect of decreasing the frequency and increasing the voltage would be net increase in stator current and the resultant increasse in winding temperate.

This will result in reduced life-span of the motor because of the rise in insulation temperature. Joule heat will increase and efficiency will come down. There would be slight increase in the motor torque and motor kW.

Register to Reply
Associate

Join Date: Jan 2007
Posts: 35
Good Answers: 1
#4

Re: Motor voltage & frequency

04/01/2008 1:35 AM

Dear Members,

What will happen if a motor designed for 415 V power supply is connected to 380 V power supply, the frequency being the same?

Regards.

R.Thiyagarajan

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5

Re: Motor voltage & frequency

04/01/2008 9:28 AM

A motor designed for 415 V and used at 380V (in both cases at the same frequency)will turn a little bit slower, (the slip will increase ...)

but the torque that the rotor can deliver will only be 84%

so the total output power is +/- 80% of the original motor.

Keep in mind that when the motor is driving the same tool at 415 and at 380V, the needed torque on the motor shaft, will be the same. The motor will, despite the lower voltage, try to deliver this needed shaft torque. So the motorcurrent will increase and the motor will warm up.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6

Re: Motor voltage & frequency

04/02/2008 12:20 AM

Nambiathiri,

The ratio of voltage to frequency should remain fairly constant. This is basic to how VFD's work--as they decrease the frequency they also decrease the voltage. In your question, the voltage is going up and the frequency going down. This is just the opposite of the desired relationship. Not a good idea, as others have noted. If you "must" do it, then make sure you have the best flow of air for cooling and that your running overload protection is set at or slightly below the motor's nameplate current.

--JMM