lightning protection for offshore facilities 2

03/31/2008 2:36 PM

I have started a memo concerning lightning protection for offshore facilities. Please feel free to comment on subject below.

Purpose:

This document is intended to address the need for lightning protection on offshore facilities

Summary:

Offshore facilities are generally all steel structures of which all major components are welded firmly to deck. This inherently provides solid grounding to superstructure of all vessels, towers, skids, buildings, etc.

In my past experience we never installed lightning protection offshore due to the inherent all steel design of facilities. I have also consulted with other senior electrical engineers about this subject and we have all came to the same conclusion that lightning protection is not required on offshore facilities.

If lightning were to strike any location on platform the structure itself would rise to equal potential thus causing no harm to personnel or equipment.

API RP 2003

5.4.4 Tank Ships and Barges

In general, a steel ship or barge can be considered to be

protected against damage from direct-stroke lightning if the

masts and other projections are adequately grounded to the

hull. On ships whose hulls are constructed of wood or other

insulating materials, a ground connection from the mast or

other projecting metallic structure to a copper plate below the

water line should be provided. Radio antennas should be provided

with a lightning arrestor or with facilities for grounding

during electrical storms.

Ships and barges are subject to indirect induced currents

and corona effects, which can cause sparking. It is advisable

to suspend loading or unloading operations and to close all

tank openings when severe lighting storms are in the vicinity.

See the OCIMF International Safety Guide for Oil Tankers

and Terminals for speciÞc information on effective protection

of tanks and barges.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate
United States - Member - New Member

Join Date: Nov 2007
Location: Land of Ahs
Posts: 36
#1

Re: lightning protection for offshore facilities 2

04/01/2008 9:13 AM

It seems like copper at the bottom of a ship in saltwater could have some corrosion issues. I would guess there could be a conductive chemical compound protective layering applied to try to avert corrosion.

Also I would guess that people on the rigs would have some faraday shield place to hide when a lightning storm covers. I've heard stories where lightning has chosen whatever path it wants including bypassing equipotential faying surfaces etc. This includes bypassing taller structures in the strike vicinity to strike where it can best gather static.

This is a very interesting subject and I wish you well in your spec writing endeavors.

__________________
Is it possible to float on light waves?
Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#2

Re: lightning protection for offshore facilities 2

04/14/2008 11:48 AM

Well I didn`t get too many responses, so here is the final information concerning this subject..

Lightning Protection for Offshore Facilities

In general, platform electrical design is based on API-RP-14F. 14F does not consider API RP 2003 or NFPA 780 as part of it except when specific sections of these documents are referenced. (They are not referenced). API RP 540 is not even listed.

NFPA 780. Section 3-16 Structural Steel Systems

3-16.1 General. "The structural steel framework of a structure shall be permitted to be utilized as the main conductor of a lightning protection system if it is electrically continuous or is made electrically continuous."

NFPA 780. Section 3.16.2. Strike termination devices

"Strike termination devices shall be connected to the structural steel framing by direct connection…"

Strike termination devices include air terminals, metal masts, permanent metal parts of structures. 3-9.3 Substitution of metals. "Metal parts of a structure, such as eave troughs, down spouts, ladders, chutes, or other metal parts, shall not be substituted for the main lightning conductor. Likewise, metal roofing or siding having a thickness of less than 3/16" shall not be substituted for main lightning conductors."

Steel structures with members 3/16" and thicker do not need treatment. Included here are cranes, structures for LO coolers, vessels, tanks…

We should be concerned with buildings and structures where the exposed steel members are less than 3/16", in particular, if they are not inside the zone of protection provided by the cranes, antenna masts or other higher structures.

NFPA 780. Section 3.14.1 Common grounding

3.14.1 General. "All grounding media in or on a structure shall be interconnected to provide common ground potential."

The platform is the grounding electrode. The various grounding systems are independently grounded to the platform. Some clients ask to ground the electrical system and equipment ground to two platform legs.

NEC 810-20 and 57. Antenna discharge units for receiving and trasmitting radio stations.

This is a clear requirement for grounding the antennas via a discharge units. Main concern is to drain static charges not to confuse it with mast grounding.

Register to Reply
Participant

Join Date: Jun 2012
Posts: 1
#4
In reply to #2

Re: lightning protection for offshore facilities 2

06/10/2012 8:50 AM

Requirements for lightning protection covered by API 14J as part of safety system with refference to API 2003 and NFPA.

NFPA 780 3-16.1 As example, lightning protection of substation. In this case, structural steel framework is a reinforcing rebar inside concreate foundation, column, etc. Air terminal located on the roof (without mast) and connected to framework as per 3-16.2. Following to 3-16.2 we'll equal potential.

NFPA 780 3-9.3 Cover requirements for conditions where steel framework is not provided. For example, Offshore platform. If you'll installed air terminal on let's say lightning pole 10m by means of welding using steel lightning pole as main conductor, then pole will potentially dangerous and to be specified as normally enargized parts/conductor/device/element with all following electrical safety requiremants.

Steel offshore platform shall not be specified as completed earthing system.

Grounding electrode shall be located underground/sea level.

Four legs of platforms can be specified as earthing electrodes if earth points located on the legs above splash zone and interconnected to main grid. Also, we should not forget step voltage phenomen. Since for platform fabrication used different materials plates, beams, pipe, etc. with different properties step voltage can take place.

Regarding necessity of lightning protection for offshore facilities we should remember about Oil&Gas industrial safety requirements - Hardous area to be protected against lightning since as per API 14J lightning is a IGNITION SOURCE.

So, for offshore facilities lightning protection required as part of passive fire protection measure.

Register to Reply
Anonymous Poster
#3

Re: lightning protection for offshore facilities 2

03/07/2009 7:44 AM

GPS, VSDs, PLCs, cathodic system, comms/signal/data, every electrical device below 400VAC and all systems under 24VDC...all are subject to insults from lightning. Careful attention to detail in areas of grounding, bonding, shielding, SPDs are required. For personal safety, detection and notification may be needed. In short, while the probability of lightning visits is low, the potential for power quality upsets is high. See the website www.lightningsafety.com for more discussion.