transmission line tower

03/31/2008 3:44 PM

I noticed that, the transmission tower construction Middle arm is longer than the upper and lower arm

Did there is any electrically or mechanically reason?

Thanks to all

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: transmission line tower

03/31/2008 4:08 PM

So that the wires will stay apart.

Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: transmission line tower

03/31/2008 5:35 PM

Cost materials needed to build tower higher to hold the same distance between lines then building the middle arms longer.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#3

Re: transmission line tower

03/31/2008 6:28 PM

Mr Looflirpa say it is to prevent big birds (Ostriches etc) from bumping their heads against the cable above when they sit on the wire below.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply Score 2 for Off Topic
Guru
Hobbies - Car Customizing - Dances with Trees Canada - Member - because I can Hobbies - CNC - too much fun Hobbies - Target Shooting - paper shreader

Join Date: Mar 2008
Location: Ottawa, Ontario, Canada
Posts: 769
Good Answers: 10
#4

Re: transmission line tower

03/31/2008 6:33 PM

Designed to maintain the mechanical requirement to prevent arching between conductors while maintaining a tower height that is manageable, and of course preventing head injuries to birds, a huge problem with different designs

__________________
Kevin "Dances with Trees" Willey
Register to Reply
Guru

Join Date: Nov 2006
Location: KnoxTN
Posts: 1485
Good Answers: 6
#5

Re: transmission line tower

04/01/2008 12:24 AM

I will have to check all three arms at the first opportunity. My assumption is that the arms are of different links to prevent a broken upper line from falling on one or more of the phase lines below.

Electrical reason rather than mechanical / structural.

__________________
Do Nothing Simply When a Way Can be Found to Make it Complex and Wonderful
Register to Reply
Anonymous Poster
#6

Re: transmission line tower

04/01/2008 1:02 AM

In my view it is to prevent a broken upper line from falling on one or more of the phase lines below and this special design gives strength to the tower.

Register to Reply
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#7

Re: transmission line tower

04/01/2008 1:12 AM

Reducing one arm to the minimum clearance with the pole will mean that material is wasted to put the other 2 at an excessive distance.

I actually haven't seen any of those but must admit that I don't even look for them. I thought the transmission line across the street from me were spaced in a straight horizontal line but they are spaced in a triangle.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Power-User

Join Date: May 2007
Location: Los Angeles area, California, USA
Posts: 202
Good Answers: 9
#14
In reply to #7

Re: transmission line tower

04/01/2008 1:16 PM

Think:

Dissipation of lateral/rotational wind loads impose on the primary tower structure accomplished by triangular relationship of conductors.........and the GROUND DISTANCE/ ark distance issue cover in other posts.

MR. GUY

__________________
If you are looking for a positive answer..it's YUP......
Register to Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#15
In reply to #14

Re: transmission line tower

04/01/2008 1:50 PM

Mr. Guy, the wind loading would be the same regardless of the configuration on the tower, as the highest loading is at 90 degrees to the wire direction. The conductors are free swinging and therefore do not play a role in the structrul stability other than adding weight. This tower is built in a vertical configuration.

__________________
Could be worse, it could be me. :)
Register to Reply
Anonymous Poster
#8

Re: transmission line tower

04/01/2008 2:08 AM

I would like to have information on line Material of transmission Line

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#9

Re: transmission line tower

04/01/2008 8:45 AM

Not necessary middle arm is always longer.

1. The clearance from other phase is a criteria.

2. Mutual inductance minimisation is another criteria.

3. Preventing droplet of water/ice to fall on bottom contor is another criteria.

Check with your TL vendor.

__________________
BNDas
Register to Reply
Guru
Hobbies - Car Customizing - Dances with Trees Canada - Member - because I can Hobbies - CNC - too much fun Hobbies - Target Shooting - paper shreader

Join Date: Mar 2008
Location: Ottawa, Ontario, Canada
Posts: 769
Good Answers: 10
#10
In reply to #9

Re: transmission line tower

04/01/2008 9:59 AM

Ice was a huge issue here about a decade back, seems the transmission lines can't carry the load of an eight inch (8) coating of ice, go figure. Tends to bring down the lines and the towers.

If memory serves the conductor is dependent on voltage, google electrical transmission lines. There is an absolute maximum, which can be seen on transmission lines with several conductors on each line, normally four (4).

I figure I spent far too long in the electrical utility business to remember all this useless information, at least to me.

__________________
Kevin "Dances with Trees" Willey
Register to Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#11

Re: transmission line tower

04/01/2008 10:15 AM

That isn't always the case. It depends upon the system voltage, tower type, terrain, span length, conductor bundle geometry, etc. In your example, the primary reason is electrical; to maintain sufficient phase to phase and phase to ground clearances under all static and dynamic loading conditions (including ice and wind loading) and to reduce the possibility of phase to phase faults. Those clearances are important at the towers as well as in the conductor spans between support structures; tangents, angles, and deadends.

You also don't mention if the tower is single or double circuit.

Another consideration is lightning shielding. Chances are the tower you noticed is also supporting one or more overhead shield wires located above the phase conductors. Although overhead shield wires often perform secondary functions; such as communications, data acquisition, monitoring and control (and may include optical fibers for those purposes) the primary function is to intercept lightning strokes and discharge them to ground thereby preventing direct strokes to the phase conductors. The shielding angle between the shield wires and phase conductors is critical to minimizing shielding failures (when lightning strokes bypasses the shield wire and strike a phase conductor).

If you have the opportunity, take a look at the EPRI Red Book (Transmission Line Reference Book 345 kV and Above) or any number of similar reference and handbooks to get an idea of the different types of lattice, guyed lattice, vee, guyed vee and other tower and pole geometries.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Car Customizing - Dances with Trees Canada - Member - because I can Hobbies - CNC - too much fun Hobbies - Target Shooting - paper shreader

Join Date: Mar 2008
Location: Ottawa, Ontario, Canada
Posts: 769
Good Answers: 10
#12

Re: transmission line tower

04/01/2008 11:33 AM

I was trying to keep it simple, having said that you are absolutely correct, there are a vast number of environmental considerations, circuit configurations and load factors. Not to mention the budget restraints, but that is another thread. Then there is the dreaded environmental assessment and the not in my back yard mentality. I remember a project that had to have tower choice changed because a well connected lobby group didn't like to look and wanted something that was less distracting, uninterrupted power supply was of course never a consideration for them, heaven forbid the lights should go out or the pool filtration system shuts off...

<Rant interrupt>

__________________
Kevin "Dances with Trees" Willey
Register to Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#13

Re: transmission line tower

04/01/2008 12:28 PM

Hi Lineman380, strickly for mutual inductance. You will notice that there are three transpostions in the line. (if any type of distance) Keeps the the phases balanced. Crazy things start happening when you start playing with the higher voltages 240kV ac and above.

There is a 240 kV line in Northern Alberta with flat spacing that runs for 450 km (280 mi) and has a problem with capacitive inductance from the earth. When first turn on, the input voltage was 240 kV. Thinking at the time that the output at the far end, with line loss, would be be about 220 kV. Wrong, turned out the output would climb to 270-280kV with an increased load. They found out because the three phases of this line ran parallel to the earth for such a distance, the capacitance of the earth induced into the line would cause this problem. The overvoltage relays would keep tripping.

You need a triangle of the phases, to lower this type of problem. Hence, the longer arm on an "L" tower.

__________________
Could be worse, it could be me. :)
Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#16
In reply to #13

Re: transmission line tower

04/02/2008 9:57 AM

The geometry is not strickly (nor strictly) for mutual inductance. In fact that's not even a major consideration. As you correctly note, phase transpositions are used on long ac transmission lines to achieve balance and reduce line losses but that doesn't require a triangular circuit arrangement. Transpositions are employed on all types of line construction. Incidently, the poster would generally have no way of noticing "that there are three transpositions in the line" because transpositions are not made that frequently.

The overvoltage problems on the long 240 kV line in Northern Alberta were almost certainly due to power factor but the coupled capacitance of the flat (h-frame) construction was only one component. Electrical transmission lines are fundamentally capacitive but loads are predominantly inductive. I suspect the loaded overvoltage problems were solved by the addition of series capacitance.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2008
Posts: 26
#17

Re: transmission line tower

04/03/2008 2:57 AM

Actually thanks to CR4 and to every body joint to answer my question, and really these answers gives us more learn and its open our thinking for many ideas.

Thanks again

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#18

Re: transmission line tower

04/06/2008 10:28 AM

from what u mention its is double circuit line.Normally middle arm is longer than top and bottom which are of same size.Under certain conditions vibrations can set of galloping of conductors and clearance under these conditions in vertical configuration becomes less.There fore its a standard practice to have longer middle cross arms in double circuit towers having conductors in vertical configuration.If u see single circuit towers with conductor in vertical formation where two cross arms on one side and one on another side or a bridge tower where conductors are in horizontal formation you won't find this.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 18 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (2); biswanath.das (1); Bluestone (2); Dances with Trees (3); Hendrik (2); lineman380 (1); mayt2u (2); Mr. Guy (1); nesubra (1); ozzb (1); Stirling Stan (1)