Anonymous Poster

process control

04/02/2008 4:39 AM

hai all ,

I need answer for why we are following 3-15 PSI and 4-20 mA while dealing with process control Instruments?

Second question is what is the difference between a Sensor and a Transducer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#1

Re: process control

04/02/2008 9:37 AM

From the little information you have provided, you are sending a 3-15psi signal to a transducer with a 4-20mA output. It should be set up electronically so that your psi setting produces a comparable digital readout.

But I really don't have enough information here.

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: process control

04/02/2008 9:49 AM

3-15 psi and 4-20 mA signals are called "live zero" signals. It offers two advantages:

  1. If the signal cable or pneumatic tubing is cut, the signal drops to 0 psi or 0 mA. This will help you in troubleshooting.
  2. If the signal cable or pneumatic tubing is cut, the system will surely go to the fail-safe mode. For example: if the 3-15 psi signal goes to a control valve. A 0 psi signal will force the valve to close (or open if it's air-to-close). Same principle applies for 4-20 mA instruments.

Of course, the "surely" only applies if the system fail-safe mode is properly designed.

As for the difference between "sensor" and "transducer", take your pick. For some people, they're the same thing. Others see them as different things. For me, it's not terribly important. At work, we say "sensor", never "transducer". Go figure.