Motor Protection

04/15/2008 6:46 AM

Dear Sir,

I want to know, what are the electrical protections we should have for motors for following capacities,

A) 75 kW High lift pump

B) 20 kW High lift pump

C) 4 kW Submersible pumps

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Motor Protection

04/15/2008 7:12 AM

All motors must have protection against 2 things as a minimum:

  1. Short Circuit, for example fuses or a circuit breaker
  2. Thermal Overload, for example an Over Load Relay (OLR).

Beyond that, you need to determine for yourself what else is important enough to you to spend the extra money on for protection. For example, many pumps in particular can be severely damaged by running in reverse, so a Phase Reversal Relay would be required. Others cannot tolerate low or high voltage conditions and require power monitoring relays as well. Many other types of pumps, such as sumbersibles, use the fluid as a lubricant so they must have low-level cutoff protection to avoid running dry. Others must be shut off long before then if there is a possibility of sucking air because they may not be self priming. Still others may have oil bath chambers and need seal-leak detection. Still others require temperature detection using thermistors or other probes in the motor and/or pump.

All of these types of protection have specialized relays designed to provide them. Some solid state protection relays can provide most, if not all, of them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#2

Re: Motor Protection

04/15/2008 7:16 AM

dear ashita

theraml over current ,under voltage ,and earth fault protection is required for up to 100 HP motors.

suresh kumar paliwal

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Motor Protection

04/15/2008 8:01 AM

In addition to the above, the Ingress Protection rating.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#4

Re: Motor Protection

04/16/2008 12:14 AM

Use 20% up rated current MCB!

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Register to Reply