GIL Vs GIB

04/22/2008 7:39 AM

Can someone advise me on what is the key difference between a GIL and GIB for a 400kV system. How does cost of equivalent XLPE cables (simialr current carrying capacity at 400kV) compare to GIL on per kilometer basis.

regards

Deepak

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#1

Re: GIL Vs GIB

04/23/2008 2:21 AM

Dear Deepak,

Kindly clarify the abbreviation "GIL" stands for what? I believe that "G" stands for Gas; "I" stands for Insulated; however, "L" needs to be clarified.

Please note that there are two common ways to connect the Gas Insulated Switchgear "GIS" to a transformer and/or OHL. Either through cables to be connected to the GIS via Gas Insulated Cable Sealing Ends, or via Gas Insulated Busduct "GIB". The later is the most commonly used method because it is safer, more reliable and durable, and requires no maintenance.

The GIB is to be connected to a transformer through SF6/Oil bushings; while, SF6/Air bushings are to be used for the connection to Overhead Lines.

I'm sorry, as I cannot help regarding the cost difference; you may refer to GIS and Cables manufacturers. However, I'm sure that the running cost of GIB is much less than for cables.

Regards,

Register to Reply
Member

Join Date: Oct 2007
Location: Dubai
Posts: 7
#2
In reply to #1

Re: GIL Vs GIB

04/24/2008 9:43 AM

With GIL we mean gas insulated lines.

Register to Reply
Member

Join Date: May 2008
Posts: 9
#3
In reply to #1

Re: GIL Vs GIB

12/30/2008 11:04 PM

Hello, did you get your reply? I saw your query belatedly. GIL--Gas Insulated Line GIB--Gas Insulated Bushing. GIL--is used like a cable to transport power to a location.In GIL bulk power can be transported. GIB--It is the bushing to connect a cable to a transformer or GIS breaker.It is for space savings by avoiding conventional structures.

Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#4
In reply to #3

Re: GIL Vs GIB

12/31/2008 1:20 AM

Hi, yes I received the reply.. Many thanks. However, I've a comment on your clarification regarding the GIB. GIB means Gas Insulated Bus-duct. This GIB is busbar (normally made of AL), enclosed inside an enclosure filled with SF6 gas. It is used either to connect the GIS with transformers or overhead lines. The interface between the GIB and transformer is SF6/Oil bushings; while, it is SF6/Air bushings in case of overhead line.

In case you are going to use cables instead of GIB, the interface between the cable and GIS equipment is SF6 Cable Sealing Ends (CSE), while it could be either cable box filled with an insulating media, or conventional cable sealing ends at the transformer side.

Again, thank you...wishing you and all of our colleagues in this forum a Happy New Year.

Best regards,

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: GIL Vs GIB

06/13/2023 7:31 AM

<...How does cost of equivalent XLPE cables (simialr current carrying capacity at 400kV) compare to GIL on per kilometer basis...>

CR4 doesn't do commercial stuff. The best thing to do is leave the entire question in the hands of a Purchasing Officer within the organisation, and see what that individual can come up with.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856