Sizing Buffer Vessels

07/19/2006 11:00 AM

Gary Brown writes:
Can anybody help me.How do you size heating or chilled water buffer vessels.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Sizing

07/19/2006 4:40 PM

Start with the fact that it takes 1 BTU to heat 1 pound of water 1 degree F. It works backwards, too.

Do you know the range of needed flow rates of chilled water? I assume you want to produce chilled water at times of low demand and use it during times of high demand. If not, then why store chilled water? It just gets warmer with time.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Active Contributor

Join Date: Aug 2005
Posts: 19
#2

refrigerated storage or flywheel tank

07/19/2006 5:41 PM

What is your heat load and what is it's cycle rate. i.e. BTU's / min. Also what is your chiller capacity. Your storage vessel has to be large enought to provide sufficient chilled water for your process. It will help to provide insulation on the tank. If the temperature of the water is critcal (chemical process) consider a mixing valve to blend return water and supply water. you will need two water pumps one for the process, one sized to provide the correct process flow and one chiller pump sized for the chillers evaporator flow)

__________________
I love NH3
Reply
Power-User

Join Date: Jun 2005
Posts: 394
Good Answers: 1
#3

Buffer Tank

07/20/2006 10:21 AM

A major reason for a buffer tank is to provide for stable control of the chiller or boiler. Normally a heating or cooling system has at least 10 minutes of chilled water or hot water in the loop. That is it takes a packet of water 10 minutes to make a circuit through the system. If there is too little mass of water in the loop, it becomes very difficult to control the chiller/boiler. For this type of problem, figure out the volume of water in the loop and heat exchangers, look at the water flow rate and get a big enough tank to get a volume that would take about 10 minutes to complete one circuit.

Reply
Active Contributor
Engineering Fields - Piping Design Engineering - Engineering

Join Date: Aug 2006
Location: Beirut, Lebanon
Posts: 13
#4
In reply to #3

Re:Buffer Tank

08/04/2006 6:51 PM

be specific as to the type of application, volumes, temperatures, etc... then I should be in a position to assist in the conceptual design and give you guidelines on detailing your engineering. Ciao