analogue loop

05/11/2008 2:39 AM

what is the maximum distance i can transfer 4-20 mA from instrument to PLC and how can i calculat this

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: analogue loop

05/11/2008 3:33 AM

Theoretically, the distance is limited only by how much voltage you have available to drive the 20mA through the cables and the load resistor. Practically, this will probably be fixed at 24V, so you can do the sums.

See the discussion in this thread (or search CR4 for "20mA") for more details.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: analogue loop

05/11/2008 4:26 AM

Yup, here are two more threads (from my own list of discussions) that asked the same question:

http://cr4.globalspec.com/thread/12395/4-20mA-Signal-from-Level-Transmiter

http://cr4.globalspec.com/thread/21144#newcomments

If you want to calculate, first find out what your PLC's input resistance is. Then calculate how much voltage will be dropped across your input when the current is at 20mA. Finally, subtract that value from your power supply's voltage. That figure will give you the maximum voltage drop across your wires. Since you have two wires (I'm making assumptions), you need to divide your calculation by two.

Okay, so now you know how much your voltage drop is across your wires, your next step is to divide that number by 0.02 (20 mA). That gives you the maximum resistance your wire length can have.

Finally, get your cable's electrical data and find out what its resistance-per-meter or resistance-per-foot (whatever) is. Divide your maximum resistance by the resistance-per-meter and you get the theoretical maximum length of wire that you can use. To be on the safe side, divide that figure by two.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Anonymous Poster
#3

Re: analogue loop

05/12/2008 1:23 PM

1.- Check your PLC I/O card specifications. Verify maximum load resistance allowed: RloadMAX.

2.- Check your field instrument specifications. Verify load resistance: Rload

3.- Check your wire specifications. Verify resistance per 100 yards for twisted pair: Rper100y.

4.- Maximum allowed wire resistance is:

RwireMAX = RloadMAX - Rload,

Maximum wire length is:

Max Wire length = (RwireMAX/Rper100y) yards. (1)

This is for twisted pair. If you use single conductor, then Rper100y is for one conductor, and result of equation (1) above must be divided by two to obtain maximum distance between PLC I/O card and trnasmitter or whatever load you are using.

Regards,

Register to Reply
Active Contributor

Join Date: Feb 2008
Location: Mexico
Posts: 10
#4
In reply to #3

Re: analogue loop

05/12/2008 1:26 PM

Sorry, I forgot to login before answering. I am GUEST.

__________________
Nestor, a.k.a. Agridulce
Register to Reply
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#5

Re: analogue loop

05/14/2008 5:10 AM

Have a look here:

http://cr4.globalspec.com/thread/18535#comment193058

regards Uwe

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Register to Reply