Reverse power Tripping

05/11/2008 5:47 AM

Dear Friends,

We are facing problem one generator trpping on reverse power. We have three generator having capacity 2.5MW ( GTG-1), 2.8 MW GTG-2)and 4.2 MW.(GTG-3) GTG-1 & 2 runnig parellel very well but GTG-3 IS TRIPPING ON REVERSE POWER after synchronizing GTG-3 with GTG-1 & 2 OR with any one.

Besides we can run GTG-3 independently without reverse power tripping. i.e. GTG-3 couldn't run in parellel with other generators.

what could be the causes of GTG-3 reverse power tripping ? how can we find the cause of tripping? We have checked relay wiring found ok.

Thanks

Kachiya

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2007
Location: South Florida
Posts: 394
Good Answers: 8
#1

Re: Reverse power Tripping

05/12/2008 12:22 AM

Can you run 1 and 3 together without tripping on reverse power? How about 2 and 3?

try to give us as much information as you can.

Orpheuse

__________________
Orpheuse
Register to Reply
Member

Join Date: May 2008
Posts: 6
#2
In reply to #1

Re: Reverse power Tripping

05/12/2008 12:33 AM

Dear Orheuse,

Thanks for your reply

No we can't run 3 with any other generator. 3 only can be run indepenendtly( on dead bus only)

Register to Reply
Power-User

Join Date: Nov 2007
Location: South Florida
Posts: 394
Good Answers: 8
#3

Re: Reverse power Tripping

05/12/2008 1:09 AM

have you tried replacing gen. 3?

Orpheuse

__________________
Orpheuse
Register to Reply
Anonymous Poster
#4

Re: Reverse power Tripping

05/12/2008 3:21 AM

Such large machine have a KW meter, please check what is the KW value at tripping time.

If KW> 100 recheck the reverse relay

If KW around 0 please check the woodward or equivalent for speed control

Register to Reply
Member

Join Date: May 2008
Posts: 6
#5
In reply to #4

Re: Reverse power Tripping

05/12/2008 6:48 AM

Dear Friends,

Thanks for replying, After sychronising GHT-3 it's not taking any active load but it's drawing reactive power from GTG-1 & or 2( which are running in paralell ) and resuted in black out. ( GTG-3 reactive power meter showing/ going up to maximum leading var before trips on reverse power)

Register to Reply
Anonymous Poster
#9
In reply to #5

Re: Reverse power Tripping

05/18/2008 4:32 AM

That is strange, if you are drawing reactive that means that the voltage is too low.

But this shall not trip the reverse power which avoids that the turbine is driven by the generator operating as synchrone motor.

When synchronizing ,the speed ( Hz) on the slave machine shall be slighty above the master and you close the breaker within the limits of +/- 10º on the synchroscope, this avoid the reverse power. After closing the breaker the speed selector to be activated on the + side to take the load.

You shall do exactly the same on the voltage adjustment to share the reactive power

If you your machine is pumping reactive load to such an extend I suspect that there is a wrong connection on your CT's .

Please give more infos about the Speed control ( Woodward) the AVR and others sytems installed.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#6

Re: Reverse power Tripping

05/12/2008 9:03 AM

IF GTG-3 works well by itself, there is no inherent damage to the generator. It sounds like the instrument wiring for GTG-3 is incorrect. It's also possible that one or more of the GTG-3 CT's are installed backwards. Since GTG-1 & GTG-2 work together, those units must be wired the same way.

I would compare the following items of GTG-3 to the same circuits of GTG-1 & GTG-2:

  • Polarity of all CT's.
  • CT phasing through each element of all CT secondary circuits.
  • Polarity of all PT's.
  • PT phasing through each element of all PT secondary circuits, including the synchronizing circuit.
__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #6

Re: Reverse power Tripping

05/13/2008 2:14 AM

I do not suspect CT polarity and PT Polarity ,if it is so, the breaker will trip even on normal individual operation for forward Power

Controller/avr/connections to be checked,best way is to interchange the controller and check .

They have to furnish information and feedback should be fast.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Commentator

Join Date: Nov 2007
Location: Western NC
Posts: 92
Good Answers: 3
#7

Re: Reverse power Tripping

05/12/2008 3:11 PM

It looks to me like you need to check your reverse power relay setting on the breaker or check out the governor on the GTG or whatever setup you have controlling the fuel to it.

Register to Reply
Member

Join Date: Jan 2009
Location: Egypt
Posts: 8
#10

Re: Reverse power Tripping

01/19/2009 8:50 AM

Dear Friends,

I am facing the same problem. I have three Gas generators A(975 KW),B(975 KW), and C(1215 Kw). G 1 & 2 runnig parellel very well but G 3 is TRIPPING ON REVERSE POWER after synchronizing G 3 with G 1 & 2.

The different is that i keep watching the Power (KW) and Power Factor [on the generator meters] during the few seconds (≈2.8 sec) befor tripping and i found P(kw) increasing, with P.F‹1, which means that no actual reverse power occure.

Can anybody help me?

Register to Reply
Member

Join Date: May 2008
Posts: 6
#11
In reply to #10

Re: Reverse power Tripping

01/21/2009 12:13 AM

Falcon,

Please Check

  • Polarity of all CT's.
  • CT phasing through each element of all CT secondary circuits.
  • Polarity of all PT's.
  • PT phasing through each element of all PT secondary circuits, including the synchronizing circuit.
Register to Reply
Member

Join Date: Jan 2009
Location: Egypt
Posts: 8
#12
In reply to #11

Re: Reverse power Tripping

01/21/2009 7:50 PM

Thanks KKKp,

The reverse power installed is CEE Static relay PTG7100, it has 3-phase voltage signal and only one phase (C.T) signal. I checked the polarity (direction of current) of this current signal and found it OK, but the problem still existing.

The current signal is coming from C.Ts inside the generator, i checked its connection (star earthed) and then connect the C.T terminals according to it.

For this relay type, the current signal is for L3 phase, can we substitute with any other phase?

Register to Reply
Anonymous Poster
#13
In reply to #12

Re: Reverse power Tripping

01/25/2009 12:10 AM

Hi Falcon,

Could you please provide history of hte gegerators, Did any major maintenance was carried out? Did you changed any major parts or relay for the generators?

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Reverse power Tripping

01/25/2009 12:12 AM

Could you please provide history of the generators, Did any major maintenance was carried out? Did you changed any major parts or relay for the generators?

Register to Reply
Member

Join Date: Jan 2009
Location: Egypt
Posts: 8
#15
In reply to #14

Re: Reverse power Tripping

01/29/2009 8:31 PM

Dear Guest,

the 2 generators (A & B) have been working for 8 years, and already they passed through normal Preventive & Corrective maintenance, so if you can specify certain equipment to trace its history i will be grateful.

Another question, there is a Load Sharing signal between the 3 generators [connected through 2 points in the speed regulator & load sharing Device "WOODWARD" can this signal cause any problem?]