reverse power protection

05/11/2008 5:50 AM

Dear Friends,

Dear Friends,

We are facing problem one generator trpping on reverse power. We have three generator having capacity 2.5MW ( GTG-1), 2.8 MW GTG-2)and 4.2 MW.(GTG-3) GTG-1 & 2 runnig parellel very well but GTG-3 IS TRIPPING ON REVERSE POWER after synchronizing GTG-3 with GTG-1 & 2 OR with any one.

Besides we can run GTG-3 independently without reverse power tripping. i.e. GTG-3 couldn't run in parellel with other generators.

what could be the causes of GTG-3 reverse power tripping ? how can we find the cause of tripping? We have checked relay wiring found ok.

Thanks

Kachiya

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: reverse power protection

05/11/2008 8:28 AM

The GTG3 is motoring when ever it is synchronized with GTG1 or GTG2.This means the the GTG3 is running at a lesser speed than the other two.

There should be governor controller for each machine and this controller will have communication between each other and this controller will control the speed of the machine.In your case the controller attached to GTG3 should increase the speed of GTG3 to match with other GTGs.

It looks like the Controller may not effective.It might be the control signal is not going to the governor.Please check the cable,termination and the controller.

May be intercommunication between the controllers missing.

To find out whether Speed raise/Speed lower signal reaches the governor,run the machine GTG3 individually and increase the speed manually by increasing the speed from controller ( there should be provision in the controller) if it is responding then the signal reaches the governor.If this is OK,then check inter communication between the controller and the voltage and frequency input to the controller.

Please check and give us more information like engine model,controller type etc I could throw more light on this matter based on the feedback

Please also let us know whether this problem cropped up suddenly or at the time of commissioning ?

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: May 2008
Posts: 6
#2
In reply to #1

Re: reverse power protection

05/12/2008 12:38 AM

Dear Friend,

Thanks for reply, Above problem starts after replacing GTG relays in all generators. but GTG-1 & 2 runnig without problem. All relays and wirings are identical and relay wiring checked twice.

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: reverse power protection

05/12/2008 12:53 AM

Details furnished by you not adequate.You have to give history for us to trouble shoot.It looks like that you have replaced the GTG relays for all the three and the problem cropped up recently.if this is true may be relay fixed to the GTG3 defective,since you have confirmed the connections are in order.Try and inter change the relays 2 and 3 and watch the performance and let us know.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: May 2008
Posts: 6
#5
In reply to #3

Re: reverse power protection

05/12/2008 6:46 AM

Dear Friends,

Thanks for replying, After sychronising GHT-3 it's not taking any active load but it's drawing reactive power from GTG-1 & or 2( which are running in paralell ) and resuted in black out. ( GTG-3 reactive power meter showing/ going up to maximum leading var before trips on reverse power)

Register to Reply
Active Contributor

Join Date: Dec 2007
Posts: 23
#4

Re: reverse power protection

05/12/2008 4:26 AM

Dear Sir,

Whenever you are paralleling there will be an option in electronic governor where in you can set minimum load. this ensures the machine will go to minimum load the moment it is synchronised, or else it will trip on Low Forward Power Realy / Reverse Power trip. Please check these setting and revert back.

rangacharya

Register to Reply
Member

Join Date: May 2008
Posts: 6
#6
In reply to #4

Re: reverse power protection

05/12/2008 6:47 AM

Dear Friends,

Thanks for replying, After sychronising GHT-3 it's not taking any active load but it's drawing reactive power from GTG-1 & or 2( which are running in paralell ) and resuted in black out. ( GTG-3 reactive power meter showing/ going up to maximum leading var before trips on reverse power)

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: reverse power protection

05/12/2008 8:43 AM

As I said earlier one of the following not working:

1) Controller

2) Communication from from controller to Engine /Alternator

3) AVR

Since you have said connections are in order,you have to check the devices viz Controller and the AVR.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster
#10
In reply to #6

Re: reverse power protection

01/06/2010 7:06 AM

dear friend this is praveen first u check wether the load is that much high to start the gtg-3 or not ,if the load is their u have to check the resistance of the damper winding

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8

Re: reverse power protection

05/16/2008 10:49 PM

What has happened ? Is the problem solved ? If so what was the problem ? Interested to know to update ourselves.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#9

Re: reverse power protection

05/29/2008 12:40 AM

Since your generator 3 is working fine as a standalone..then i would suggest

a) Check again the wiring of reverse power relay.

b) If convinced that the wiring is perfect, change the relay.

c) Check AVR (see whether the voltage of GTG3 is increasing ..after you synchronise, i suspect the voltage is shooting up..) ..and the load sharing signal wires of Gen-3

d) In case you have a stepup transformer at the output of the generators check that they are all at the same tapsetting..usually at Tap 3.

More importantly give feedback...

cheers...

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Anonymous Poster
#11

Re: reverse power protection

01/06/2010 7:14 AM

dear friend in ur problem their is no defencicy of power in the circuit their is excess of power flowing in network then only while ur starting the gtg-3 its thking that excess of power & running as motor please check the starting system of the gtg-3

Register to Reply Off Topic (Score 5)
Anonymous Poster
#12

Re: reverse power protection

01/06/2010 7:22 AM

their is no defiancy of power in network their is excess of power flowing in the network then only gtg-3 is running as motor

Register to Reply
Anonymous Poster
#13

Re: reverse power protection

01/08/2010 6:19 AM

dear friend their is problem with excess of power than only that gtg3 taking that power & running as motor so please change the conditions in amf module

Register to Reply Off Topic (Score 5)