CT Rating for kwh Meters

05/12/2008 5:45 AM

How do you properly size up/compute the CT for kwh meters?

__________________
Pleasure in the job puts perfection in the work. - Aristotle
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: CT Rating for kwh Meters

05/12/2008 5:58 AM

This is very simple.Kwhr meters are available for 1 Amp or 5 Amps.therefore CT Secondary should be either 1 or 5.The primary of CT should be greater than the Maximum Primary current rounded of to nearest hundred. supposing the maximum primary current is 920 Amps the CT ratio is to be 1000/5 or 1000/1.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: CT Rating for kwh Meters

05/13/2008 2:35 AM

Actually, best practice is to size the CT ratio to have the expected normal load fall into the middle of the range. This is where the CT's accuracy is best and most stable under temperature variances. It also allows more head room for overloads. If you put a 920A continuous load through a 1000:5 CT, whenever something inductive turns on it will drive the CT into saturation. So for a 920A normalized load, I would use a 2000:5 CT (or 2000:1 if the WHM needs a 1A input).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: CT Rating for kwh Meters

05/13/2008 3:50 AM

Dear sir

Thanks for your comment and well taken, I have mentioned Maximum permissible current as an example for the persons to understand.It was not normal current.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: May 2008
Location: Philippines
Posts: 3
#4

Re: CT Rating for kwh Meters

05/13/2008 11:17 AM

Thanks for the information kind Sirs. I have an additional inquiry.

If I have a total computed load of, for example I = 630A, I could still use the 1000:5 CT rating? (If my meter requires 5A).

__________________
Pleasure in the job puts perfection in the work. - Aristotle
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: CT Rating for kwh Meters

05/13/2008 3:49 PM

Yes, it would work fine, but again, I would opt for a 1200:5 if possible.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

fmsantiago (1); JRaef (2); ramvinod (2)

Previous in Forum: 63A Receptacles   Next in Forum: Voltage Regulator
You might be interested in: Utility Meters, Flow Meters, Lux Meters (Light Meters)

Advertisement