05/13/2008 3:29 AM

We come accross in electrical engineering protection siganls such as breaker lockout protection, gas pressure low lockout alarm. What is lockout all about? what will be done by operator in control room when this alarm appears?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: lockout protection

05/13/2008 8:05 AM

<What will be done by operator in control room when this alarm appears?>

This is defined in the Control Philosophy document for the plant, which is an output from a design process that will probably be based upon a 'HazOp analysis' at well-run installations. The information is therefore installation-specific, and should be there 'higher upstream'.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#2

Re: lockout protection

05/13/2008 9:25 AM

In electrical protection signals lockout sometimes called (Ansi device number 86) refers to a manual reset only switch which operates when the electrical equipment protection relaying or instrumentation detects fault. This will require operator when receiving alarm to dispatch electrician to location to troubleshoot fault, and when fault has been found and repaired he will then manually reset the 86 lockout relay.

The low gas pressure lockout will be referring to either SF6 gas pressure or transformer nitrogen blanket, depending on which type of equipment you have in your plant. If the gas pressure hits low-low setpoint it will activate lockout relay and trip breaker isolating equipment in question.