Close Transition between Main Power Supply and Generator

05/22/2008 12:54 AM

Refer to the question,I would like to ask about this matters.

FYI, we ere currently installing a ACTTS , or Auto Close Transition Transfer Switch, or ATS. During the close transition (transfer load) from the main supply( In Malaysia, we are provided by Tenaga Nasional Berhad) to the Standby Generator , the power dip occured in very short time< 1second. I suspected UnderVolatge Trip at Generator, but the UnderVolatage relay not detected. hmm what actually can effect the dip? we measure the Voltage, is OK. How about undervoltage coil? or another possible caused?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#1

Re: Close Transition between Main Power Supply and Generator

05/22/2008 5:25 AM

A standard ATS will always give a voltage dip because it disconnects the one supply from the load before transfering to the other supply. if you want bumpless tranfer you need to sychronise the supplies together before switching one of them off.

If you are using generator as mains failure only you will always get a dip

__________________
A day without a smile is a day lost
Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#2

Re: Close Transition between Main Power Supply and Generator

05/22/2008 8:19 AM

I presume what you observed was your standby generator being reverse powered by the grid..

The next time you transition observe your KW meter on standby genset, and look for power flow in the negative direction, also observe your reactive power (VARS) in the same fashion.. A couple of questions..

How long is your closed transition timer set for? Normally this can be very short..

How big is you standby gen set?

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Close Transition between Main Power Supply and Generator

05/22/2008 11:35 PM

Has the DG source tripped ?.If it is tripped then there is a problem which has to be probed thoroughly.

If it is only dip, it is bound to happen, as the Mains supply will be cut off and DG supply will be switched On in a fraction of second.

If you do not want any dip in voltage, you should first synchronise the DG supply to the Mains , transfer the loads to the DG source and trip the Mains supply.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Participant

Join Date: May 2008
Posts: 2
#4

Re: Close Transition between Main Power Supply and Generator

05/23/2008 12:09 AM

Hi everybody, thanx to All for ur respon. After some troubleshooting, we found that no problem actually on our existing genset, the problem was caused by the new ACTTS installed. some setting on that equipment. problem eliminated already.tq once again

Register to Reply
Participant

Join Date: May 2008
Posts: 1
#5
In reply to #4

Re: Close Transition between Main Power Supply and Generator

05/23/2008 3:24 AM

Owh...so the conclusion is setting on that equipment....

Well done.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#6
In reply to #4

Re: Close Transition between Main Power Supply and Generator

05/27/2008 9:42 AM

Just curious, ainahamd,..but what was that "some setting"...it would be great if you can share that info with the forum members once you find it...

Cheers

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire