Grounding test lead lengths

05/27/2008 11:51 AM

In using a four probe testing configuration and applying the Wenner formula to the test results, does it matter that the lengths of the test leads are different by large lengths: 125ft, 250ft, 500ft, 1000ft? How about if all were 500ft, but the ohmage per reel was .1 ohm different?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#1

Re: Grounding test lead lengths

05/27/2008 11:47 PM

4-probe testing,

What are you testing? I'm sorry, but that isn't clear in your question.

If electronics, why such long leads?

Are you doing 4-wire testing like for a low value resistor or in circuit component?

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Member

Join Date: May 2008
Posts: 8
#6
In reply to #1

Re: Grounding test lead lengths

05/28/2008 11:52 AM

I'm testing for the soil resistance at a new substation site. I am using the Biddle DET 2/2 tester. A very good value is around .5 ohms. A few of the additional threads have some pretty good answers to the lead length question. Thanks.

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#2

Re: Grounding test lead lengths

05/28/2008 12:27 AM

Do you mean a Kelvin bridge configuration which has two current wires and two voltage sensing wires to make very low ohms resistance measurement such as contact resistance in switch gear for power distribution systems..

Current is the same in all parts of a series circuit so the current leads are not critical. However, it would be better to have the voltage leads of equal lenght. In theory that is.

In practical real world situations, you run the risk of introducing inductive pickup of voltage in the voltage sensing leads.

Why such long leads. Even big switch gear seldom needs moe thantwo ten foot lead sets. That is what I used on my test gear. And yes I di duse shielded cables to minimize noise pickup.

__________________
Elnav
Register to Reply
Member

Join Date: May 2008
Posts: 8
#7
In reply to #2

Re: Grounding test lead lengths

05/28/2008 11:59 AM

It is not the Kelvin bridge configuration... but close. It is the "Line Traverse" method of measuring for soil resistivity. The probes (or stakes) have distances as large as 300 to 800 feet apart according of an example of a Nomogram for resistivity calculations in the DET 2/2 tester manual. Later threads have some good answers to my question I think. thanks.

Register to Reply
Power-User

Join Date: Apr 2007
Location: n. Switzerland
Posts: 133
Good Answers: 6
#3

Re: Grounding test lead lengths

05/28/2008 1:47 AM

I call your attention to the 2nd line

http://cr4.globalspec.com/edit/newthread?pt=1

-rfg

__________________
Regards, RF_guy
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#4

Re: Grounding test lead lengths

05/28/2008 7:43 AM

For other readers of the thread The Wenner formula is used to calculate soil resistance:- here's a link to a general description:-

http://www.netaworld.org/files/ItemFilea837.pdf

Mejic,

The reason for using four probe measurements is to eliminate the resistance in the test leads from the measured result.

Wires A and B are attached to one probe C and D to the other. (When I say probe I mean stake in the ground: in normal electronic applications you need to use four probes to eliminate the contact resistance).

...............A,B.................................................C,D.....................

Drive a known current from A to D

Measure the voltage from B to C

Calculate the resistance using Ohms law (V=IR, so R = V/I). Apply Wenner's formula.

Now as long as the resistance in the A and D leads (and probably much more significantly in your case: the sample) does not prevent you from driving the required current, and the resistance in the B and C leads is considerably less than the input impedance of the voltmeter you can't really go wrong.

Digital multimeters typically have an input impedance of 10 MΩ. So a few Ohms in the test leads won't make any difference.

Does this make sense?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Member

Join Date: May 2008
Posts: 8
#9
In reply to #4

Re: Grounding test lead lengths

05/28/2008 1:02 PM

Excellent answer. The tester is apparently a "current source" which means the test lead resistance doesn't matter for the two "C" probes. The tester senses the resulting voltage from the "P" probes and the lengths also do not matter since the ohmage of the tester is "infinite" and all of the voltage will be sensed by the tester. This thread business is very good. Thanks everyone.

Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#5

Re: Grounding test lead lengths

05/28/2008 8:21 AM

The test leads that come with your test set have been calibrated to it at the specified length.. I would check with mfg of test set before modifying..

Here is a good article on ground testing..

http://www.netaworld.org/files/ItemFilea837.pdf

What mfg of ground tester are you using??

Register to Reply
Member

Join Date: May 2008
Posts: 8
#8
In reply to #5

Re: Grounding test lead lengths

05/28/2008 12:20 PM

The tester is the Biddle DET 2/2 and it did not come with test leads. We had to make our own. I called the mfgr and from them and of the thread answers here, it appears the lengths do not matter. The tester is apparently a current sources and will pump out a certain current regardless of the resistance of the lead lengths. Thanks to all.

Register to Reply
Member

Join Date: Jul 2011
Posts: 9
#10

Re: Grounding test lead lengths

07/28/2011 11:27 PM

CR4 ADMIN: Deleted Post


Spam:
This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.