Low voltage class one and two at 12 watts

05/27/2008 5:12 PM

Is class one wiring required for a circuit that has a 200 va 24 VDC power source with a 0.5 amp fuse. I need to prove that it is or is not to a consultant.

There are numerous systems installed all over the country that do not have class one wiring all the way to the load from the source and (do) have over a 100 va power source.

I can take my answer off the air thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Low voltage class one and two at 12 watts

05/27/2008 6:47 PM

I can take my answer off the air thanks.

I didn't know we were on the radio...

Just because things exist does not make them legal...

Anyway, this website actually is a pretty good primmer on wiring class issues. I suggest you read it.

http://www.electrician2.com/eltrain05/lpage104.html

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2

Re: Low voltage class one and two at 12 watts

05/27/2008 7:51 PM

Hello Guest,

You refer to: <"....numerous systems installed all over the country....">

You do not bother to state to which actual Country you refer.

Please reply, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#4
In reply to #2

Re: Low voltage class one and two at 12 watts

05/29/2008 8:08 AM

I read that link for my own satisfaction and found it rather convoluted. If I am reading it correctly it would seem to say that for anything over 100VA then Class 1 wire is required and that using a fuse to "lower" the current rating doesn't count. That's probably because you could get a heart stopping shock in less time than it takes the fuse to blow?

There is also a general prohibition against running Class 1 & Class 2 in the same conduit or raceway. That was pretty clear.

Do I have that right?

__________________
Eric
Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#5
In reply to #4

Re: Low voltage class one and two at 12 watts

06/19/2008 11:47 PM

never rely on a fuse to save your life, I have bridged a 240VAC load once with my hand, shattered a 10A-3AG fuse leaving me with a sore hand and 2 end caps still in the fuse holder.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#3

Re: Low voltage class one and two at 12 watts

05/29/2008 12:13 AM

Is the consultant your customer?

Generally, in the company I work in, we wire to the standards setout by the customer, each customer is different.

Have the customer supplied fully their intentions and you have spoken to them concerning the reasoning of their wishes/desires?

People on here could say, "No its not specificially needed" but what you supply to your customer should be as close as possible to what they asked for.

Class 1 or no class 1, its up to the customer to decide which way they wish to go, but also remember, the quote should also reflect the price differance if there is a selection of classes, this could also sway their descision as to where they wish to go.

If you say that Class 1 is the same price as none, they will go for Class 1.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake