Selection of Generator

05/30/2008 6:15 AM

I am in the process of selecting a Diesel generator for running plastic porcessing machineries. There has been contradicting suggestions. Kindly give me your suggestions.

-Devarajan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Selection of Generator

05/30/2008 6:55 AM

Please describe the contradicting suggestions.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: May 2008
Posts: 7
#2
In reply to #1

Re: Selection of Generator

05/31/2008 12:00 AM

DC load to be multiplied by 4 or 2?

generator to be selected for maximum load or the practical 60% load?

Total KW to be the load selection criteria?

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: Selection of Generator

05/31/2008 12:43 AM

DG set selection is based on

1) Load to be connected

2) Types of load

3) Method of starting of drives

4) Sequence of starting

May be we can help you in selection, provided you furnish all the particulars mentioned above.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: May 2008
Posts: 7
#4

Re: Selection of Generator

05/31/2008 11:57 PM

Total DC load is 225.15KW

Total AC load is 722.7Kw

Total Heater load is 314.09Kw (single phase)

DOL starters only for motors of utilities below 5HP

AC variable frequency drives for plant drives irrespective of HP

No Sudden ramping up/down for any drives other than Utilities

Plants start up gradual and no sudden loads.

-devarajan

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5
In reply to #4

Re: Selection of Generator

06/01/2008 2:15 AM

1) How are you converting AC supply to DC supply-Method ?

2) Can you not distribute the single phase Heater load equally to all the three phase ?

3) The loads should be distributed to all the phases.You can not have 50 % of the load as single phase.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Member

Join Date: May 2008
Posts: 7
#6

Re: Selection of Generator

06/01/2008 2:47 AM

the drives are SCR controlled supplied by ABB and Siemens.

The heater loads are distributed on to three phases, but when the Die heads are changed there may be minor imbalances

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7
In reply to #6

Re: Selection of Generator

06/01/2008 7:44 AM

Can you explain and give more details of DC Loads.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply