I am getting flucuating pressure and volumes at my booster station because of a set of valves in a municipal valve pit about five miles away. That pit has a 3" valve which operates under normal flow conditions and an 8" valve that opens and closes as needed to meet demand, (based on pressure drops). The problem is that a wave is created between the suction side of my fire pump and the valves in the municipal pit five miles away. Any way to modulate the wave and smooth out my suction pressure and supply?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Posts: 479
Good Answers: 9
#1

Re: Wavering

06/03/2008 1:49 PM

You need a fire-flow bypass. During the fire, flow is through the 8" bypass. Normally, the bypass will be closed and flow will be through the 3" likely a venturi meter.

The bypass needs to be automated.

Please tell us which side of the booster this valve pit is (suction or discharge).

Register to Reply
Participant

Join Date: Jun 2008
Posts: 3
#2
In reply to #1

Re: Wavering

06/03/2008 4:11 PM

Suction side of the booster. The water originates in a tower. It goes down to the municipal valve pit where it passes through either the 3" or 8" valve depending upon demand. Then it travels through an industrial park, branches off to residential areas and ends in a dead end at my booster station.

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#3

Re: Wavering

06/03/2008 4:13 PM

Here is how I understand your problem

When the demand increases, and the pressure drops, your booster station's fire-pump engages and demands more from the city pit, the city pit opens its large valve and provides allot of pressure which in turn shuts off your pump. The flow is reduced so the city pit shuts down to the smaller valve, the demand is not met, so the cycle repeats, over and over again.

In other words the city pit is providing more water then your booster pump can handle, or your booster pump is engaging too soon for too small of a demand change.

You may want to have your pressure sensors and relays re-calibrated until the demand or pressure drop is is greater, or slightly delay pump engagement.

Best fix would be to add a pressure regulating tank, or water tower between the source and your booster station.$$$

__________________
Perfection is a subjective and abstract concept.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#4

Re: Wavering

06/03/2008 5:39 PM

There are a number of solutions to attenuate pressure waves in the system. Typically you would employ a pressure tank or a release valve in a situation like yours. These systems absorb or attenuate the pressure wave as it travels through the system. another thing to consider is that the 8 inch valve is just opening too fast, and maybe it can be slowed down in response time (or a different valve system may be employed that repsonds a little slower). This would mean you build pressure slower, but you would not have the huge pressure surge.

Register to Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#5

Re: Wavering

06/05/2008 12:07 AM

Have you tried installing a hydraulic accumulator on the pipeline?

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Civil53 (1); DVader1000 (1); RCE (1); techno (1); user-deleted-9 (1)

Previous in Forum: Gap between vessel saddles and top of the foundation   Next in Forum: What is the Concrete Cube test relationship to Concrete Core test

Advertisement