Fault Level

06/04/2008 11:20 PM

hi,

iam an electrical technical officer. got no qulification certificate or anythings, just base on my experiance. just wondering what this fault level that so important when designing power distribution. am always been asking by my senior on this. cant answer him correctly. and how to calculate it?

thanks for any respond and especially knowladge.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Fault Level

06/05/2008 12:13 AM

Kindly register yourself and identyfy, give your email id, the brief write up on fault level etc can be sent to you.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply Score 1 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Fault Level

06/05/2008 12:24 AM

<cringe>

__________________
jack of all trades
Reply Off Topic (Score 5)
Anonymous Poster
#3

Re: Fault Level

06/05/2008 1:07 AM

The fault level at a point is that current which would have caused 100% voltage drop, upto that point, in case, a bolted-type-arcless zero resistance short-circuit is created at that point.

An example - A system fault level at a point is 125 MVA. Then system impedance upto the point is 1/125 = 0.008 p.u. per MVA or 100/125 = 0.8% per MVA.

Dear guest nothing is difficult to learn - there should be desire in you to learn. However to learn this subject your basic understanding of AC system is necessary and good knowledge of mathematics. Short circuit calculations are simple provided basic knowledge is gathered.

Do not hesitate to identify yourself. The forum tries it best to help all.

Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4

Re: Fault Level

06/05/2008 2:40 AM

Tell your employer, if he sends you on a basic relevant study course it will benefit both of you and you will then be able to answer his question.

Find the course you wish to attend first (prefferably day release with maybe an evening class too)

Most of my education relevant to Electronics was done like this.

Del

__________________
health warning: These posts may contain traces of nut.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Fault Level

06/05/2008 3:02 AM

Job-related training is an important investment for any business.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#6

Re: Fault Level

06/06/2008 12:55 AM

Fault Lvl Calculation :

01. Main Xmr - 6 MVA , 66/11 KVA , 7.75 % impedence.

02. Cable 300 sqmm, HT , XLPE - 20 mtr.

First convert all component in to per unit MVA rating.

(A) Xmr 6000 KVA :-

MVA value = MVA rating / Impidence (Z)

MVA value = 6 / 0.0775 = 77.41 MVA

(B) 66 KV Cable MVA :- MVA Value = MVxMV / Z

MVA Value = .066x.066 / 0.002, assuming Cable impidence is 0.2,

MVA Value for cable = 2.178 MVA

Total System MVA ( Fault level ) = A + B = 77.41+2.178 = 79.588 MVA say 80 MVA

Reply Score 1 for Good Answer
3
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#7

Re: Fault Level

06/06/2008 2:51 AM

It's important because it tells you what the maximum current will be if there is a total short circuit in the circuit. It depends on the impedance of the supply alternator, transformers and feeder cables.

Imagine a forklift rams its tines into a factory distribution board just above the local circuit breaker. For a short time (before the main board's protection acts) there will be a huge current (the fault level) and this may cause significant heating or mechanical effects ie melting terminals or ripping the cables from the cable tray.

The high fault current can also cause arcing as the contacts open, the arc burns the circuit breaker and the resultant gases allow the arc to continue, etc followed by BANG! the switchboard blows up.

Circuit breakers have a fault rating that they guarantee to break without damage.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Reply Good Answer (Score 3)
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: