Transformer Unbalance - Open CKT Voltages

06/05/2008 9:35 AM

in one of our furnace trafo 45mva,33kv/750v , when i checked open ckt voltage i found 500/700/750v.this transformer secondry is connected to heating electrodes through water cooled busbars and these busbars are supported on insulators.what may be the reasons.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#1

Re: transformer unbalance open ckt voltages

06/05/2008 2:11 PM

When you say open circuit voltage, I assume the electrodes are disconnected??

Is the voltage measurement to ground reference?

Is there a heavy current unbalance when the transformer is in service?

Reply
Anonymous Poster
#3
In reply to #1

Re: transformer unbalance open ckt voltages

06/12/2008 6:04 AM

Hi,

Open Circuit Volatge means when the transformer is supplied with a voltage on the HV or LV side ( 1:1) Transformer, then Open Circuit means the transformer is under no load.

Voltage measurement shall be Phase to Phase, Phase to neutral.

Current Unbalance shall be unbalance in load. The differntial relay will operate during current unblance as this protection will be based on Unbalance current.

N.Suresh

Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#2

Re: transformer unbalance open ckt voltages

06/05/2008 2:21 PM

Is the incoming line voltage balanced?

If everything looks good, then it sounds like your transformer has shorted turns. I would recommend taking out of service and perform..

1- winding resistance

2- TTR Transformer Turns Ration

3- Power Factor Test if available

Then compare against factory tests..

Reply
Associate

Join Date: Jun 2008
Location: Chennai
Posts: 31
#4
In reply to #2

Re: transformer unbalance open ckt voltages

06/13/2008 2:53 AM

Hi,

If incoming line voltage itself is low/unbalanced then it shall be adjsuted in the sending end substation by balcning the load and the rasing the volatge. Raising/ lowering the voltage shall be done by adjusting the Tap cahnger in th trafo.

Alterantively the Voltage in the Bus can be improved by by providing Bus capacitor bank.

N.Suresh

__________________
N.Suresh
Reply