Steel Skywire - Short Circuit Capacity

06/05/2008 11:23 AM

Hello,

When doing grounding studies, it is common practice to calculate the amount of fault current that will return to the source through the skywires and distribution neutrals when calculating the GPR. However, does anyone ever compare the short circuit capacity with the expected fault current through the skywires to see if they can handle the amount of current.

I received data for a OPGW cable that is used for a generating station that I am analyzing and it has a short circuit capacity as 33000 Amps^2*sec which is only 256 Amps for a 0.5 second fault. The fault current levels that I calculated that will be going through the skywires is much higher. Am I interpreting this correctly?

The skywires are meant for lightning protection and given the very short duration (usec) they are OK but for a power system fault it doesn't seem very good.

Is anyone have any experience or knowledge on this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Apr 2008
Posts: 41
#1

Re: Steel Skywire - Short Circuit Capacity

06/07/2008 3:48 AM

HI

I also want to know the same thing

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Steel Skywire - Short Circuit Capacity

06/12/2008 6:37 AM

Hi,

The Shield wire and the Lightning Spike is generally designed based on the highest short circuit current of the system. For ex. (if a system is designed for 50kA or 40 kA for 1 sec) as well the zone (area/ the respective equipemnts in that area) to be protected. 45 deg. protection of a particular zone is considered for Direct Stroke Lightning Protection Claculation.

N.Suresh

Register to Reply