Mains power factor correction and diesel generator

06/11/2008 12:28 PM

I have power factor correction fitted on our mains supply (don't know the size) and was going to get a backup diesel genny until somebody told me that the pf unit needs to be switched out of the circuit before the genny can takeover on a mains failure otherwise major damage can be caused. Is this true?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Mains power factor correction and diesel generator

06/11/2008 1:13 PM

It depends whether power factor correction is capacitive or inductive.

From This white paper by Jim Iverson, Senior Applications Engineer:

"Power factor (PF): Capacitive loads, overexcited synchronous motors, etc. cause leading power factor, where current leads voltage. Generators have a very limited capacity for supplying leading power factor loads. If not controlled, these can
lead to loss of voltage control and damage to the generator. Lagging power factor, where current lags voltage, is more generally the case and is a result of the total inductance of the circuit. Power Factor is the ratio of kW to kVA and is expressed
as a decimal figure (0.8) or as a percentage (80%). Three-phase gensets are rated for 0.8 lagging PF loads and single-phase gensets for unity power factor loads. Lower power factor loads require larger alternators or gensets to properly serve the
load."

This indicates that the correction is required in the cct.

It also depends whether the correction is for the load, or supply lines.

A correction for load will bring the loads close to PF of 1. The only way I can see this as a problem is if a capacitor in the correction feeds back to the automatic switching ccts after power is lost. There are switches specifically designed to handle live switching.

If it is for the power lines, yes it needs to be switched out, but more likely it is for your load matching.

__________________
Perfection is a subjective and abstract concept.
Reply Score 1 for Good Answer
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#2

Re: Mains power factor correction and diesel generator

06/11/2008 1:32 PM

If it is for the power lines, it belongs to the power company. In this case simply have the connection point for switch over to your generator after the PF correction unit.

__________________
Perfection is a subjective and abstract concept.
Reply
Power-User

Join Date: Mar 2007
Location: Bangalore, India
Posts: 141
Good Answers: 1
#3
In reply to #2

Re: Mains power factor correction and diesel generator

06/12/2008 12:34 AM

I need to know more details

1) Whether the power factor bank is switched on after the diesel generator talkes over the load.

2) Is it automatic or manual

3) I sit always switched on even if there is no load.

It is generally recommended to have after the genertaor reaches its peak and connected to bus bar.

__________________
Best Regards, Shivaram
Reply
Anonymous Poster
#8
In reply to #3

Re: Mains power factor correction and diesel generator

07/10/2009 10:08 AM

I want to connect a power factor correcting equipment with my 591 kva diesel Generator to improve its p.f from 0.8 to 0.98. Then what will I have to do?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #8

Re: Mains power factor correction and diesel generator

02/19/2024 8:05 AM

Find someone locally who can do it. Internet search, then telephone, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Jun 2008
Location: kolkata
Posts: 63
Good Answers: 2
#4

Re: Mains power factor correction and diesel generator

06/12/2008 1:13 AM

True, but it depends on power factor KVA rating vis a vis Generator reading. When you start the Genset and have not loaded it yet then all the loading will be capaciatnce from the Genset , if the panel is directly in contact with powerfactor correcting device. After you have taken the Loads in the generator , you can use the Powerfactor correction with Genset. Generally Generators are rated with lower Power factor , say 0.8 when they show the KVA rating with respect to the Kw power of the Engine . So, if the KW power of Engine is 100Kw , then the Alternator Rating is given as 100/0.8 = 125 KVA. So it is better the power factor correction panel has a switch unit also. After loading the set with the loads it is to take , then PF corrector switched be made on.

Reply
Anonymous Poster
#5

Re: Mains power factor correction and diesel generator

06/12/2008 8:42 AM

Provide a transfer switch wiring scheme that cuts out the capacitor bank, if possible, when the generator is running. And yes it can damage the generator.

Reply
Anonymous Poster
#6
In reply to #5

Re: Mains power factor correction and diesel generator

06/13/2008 7:49 PM

Been there ... done that. Unless you are connected to the utility company source, you better have a place for capacitor vars to go. If you don't... the vars will try and feed back to the generator and mess it up. Automate the capacitor or keep it off.

Capacitor Bob

Reply
Anonymous Poster
#7

Re: Mains power factor correction and diesel generator

06/17/2008 4:26 PM

The cap bank should have a disconnect switch/contactor on the primary sie. Loop the control voltage for that device through the EG ATS or breaker scheme secondary contacts this will disconnect the caps as long as the EG is supporting the load.

Note: Caps need to have a way to bleed off excess voltage. If you don't bad things could happen when they reconnect.

Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#9

Re: Mains power factor correction and diesel generator

07/30/2009 9:35 AM

hello friends, pls tell me why it is not advised to operate PFC capacitors and gensets together, what is the biggest drawback? There are so many idea but pls tell me the real ones..

__________________
jinxnao
Reply
Participant

Join Date: Dec 2009
Location: NRSC HYDERABAD
Posts: 2
#10
In reply to #9

Re: Mains power factor correction and diesel generator

12/08/2009 4:18 AM

If automatic power factor correction equipment is used ,it can be connected to gensets also without over loading gen set. As a precaution PF Value can be set at.95 when on gen set.

Reply
Anonymous Poster
#11
In reply to #9

Re: Mains power factor correction and diesel generator

12/08/2009 8:26 AM

You do not want the power factor (to be supplied by the Gen) to go into leading mode. The armature magnetic field leading the field is a bit bad for the stability of the Gen. There are quite a few papers on this aspect. Keeping it too near the generator may land up in this problem and you may have problem in controlling the hunting.

Reply
Participant

Join Date: Mar 2012
Posts: 1
#12

Re: Mains power factor correction and diesel generator

03/23/2012 8:39 AM

can pf correction work together with a diesel gen .what can i do to rectify problem

Reply Off Topic (Score 5)
Reply to Forum Thread 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); chakraborty ranabir (1); deon kruger (1); jinxnao (1); KONDAL GOUD (1); PWSlack (1); shivaganti (1); techno (2)

Previous in Forum: NEC codes   Next in Forum: electricity

Advertisement