Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/17/2008 10:28 AM

I have differential-pressure transmitters serving as "level" transmitters for cryogenic (liquefied gas) storage tanks, with the vapor side feeding the LOW input and the liquid side feeding the HIGH input. Since it is problematic for me to pressurize the LOW input during calibration, I have been calibrating the transmitters with the LOW side open to atmosphere, and the HIGH side pressurized with a calibrated pressure source to a value (expressed in inches of water) listed on a spec sheet that supposedly represents full-tank conditions under constant, "idealized" pressure. (One set of tanks contains liquefied oxygen, with a nominal tank pressure--and therefore vapor-side pressure--of around 40 psi. The other set of tanks is liquefied carbon dioxide, with a nominal tank pressure--and therefore vapor-side pressure--range of 280-290 psi, varying as a pressure-build system responds to pressure switch controls.) If I continue to use my present methodology of opening the LOW side to atmosphere while calibrating the HIGH side, how can I enhance the accuracy of my level readings once the DP transmitters have been re-pressurized with actual tank vapor-and-liquid values (this issue is especially confusing to me with the LOX, since I have a chart that shows different tank level readings for the same differential pressure value that change depending on what the actual--i.e., vapor-side--pressure is)? After calibration, the DP "level" transmitters seem to read about 3-6% lower than parallel-mounted mechanical gauges indicate. Am I doing something wrong?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/18/2008 8:05 AM

the HIGH side pressurized with a calibrated pressure source

Hmm, does your "calibrated pressure source" have a calibrated pressure gauge that will show you the actual pressure it's putting out? At least that way, you'd know what pressure you're injecting into the High side with respect to the atmosphere which is what your Low side has.

Further, is your transmitter at the same level as the lower tap? If it's higher or lower, your zero will change when you reconnect the transmitter to the tank.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Participant

Join Date: Jun 2008
Posts: 3
#4
In reply to #1

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/18/2008 12:48 PM

Vulcan:

Many thanks for the tips--my pressure source is indeed equipped with a readout, and is calibrated to NIST specs. I had not paid attention to potential elevation/depression offsets, however, and will take that into account at my next calibration (my initial instinctive response is: I need to do more research. These are very tall, vertically-mounted tanks, with capacities of 26,000 lbs for the LOX and 52,000 lbs for the CO2, and I think that the vapor-side inlet is physically higher than the liquid-side tap).

Again, thanks--Toltec

Register to Reply
Associate

Join Date: Jan 2008
Location: USA
Posts: 38
Good Answers: 2
#2

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/18/2008 8:47 AM

As Vulcan said, pay special attention to the physical location of the dp sensor and routing of the sening lines. Fully understand the impact of liquid head. Where will the cryogenic liquid be vaporized in the sensing line if using direct sensing? If using capillary lines and diaphragms, remember to account for liquid head in the capillary.

I presume all fluids are saturated so temp and pressure are not independent. As such, the density of the liquid may change significantly with temperature / pressure. In this case, a true level sensor and d/p cell will not react the same to a change in density.

Manufacturers will say a d/p cell is not sensitive to absoulte pressure, and in my experience, this is true.

__________________
All generalizations are false, including this one.
Register to Reply
Associate

Join Date: Jan 2008
Location: USA
Posts: 38
Good Answers: 2
#3
In reply to #2

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/18/2008 8:51 AM

You may also need to pay special attention to the temperature ratings of the d/p sensors. If the sensor is exposed to the cryogenic temps, it may exceed the temp rating of the instrument. You can protect agains this by a well designed sensing line, but always know the impact of liquid head in the sensing line.

__________________
All generalizations are false, including this one.
Register to Reply
Participant

Join Date: Jun 2008
Posts: 3
#5
In reply to #3

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

06/18/2008 1:01 PM

Worksalot:

Thanks for the tips--unfortunately, I do not have report back on the temperatures inside the tanks, only the vapor-side pressure, but I am fairly confident in those readings (the insulation quality of the vessels is inspected/verified annually). I will certainly review the temperature specs of my d/p sensors. I am unfamiliar with determining the effects of cryogenic liquids in the sampling lines (especially with where they may be changing density), but I have been curious as to whether the instrument sample feed lines, being exterior to the tanks, uninsulated, and exposed to varying ambient temperature (about 10' or so of total tank-exterior lines) could be contributing to my post-calibration inaccuracies. I've got some research to do!

Much obliged to you and Vulcan for your help--Toltec.

Register to Reply
Anonymous Poster
#6

Re: Calibrating DP-Type Level Transmitters for Cryogenic Tanks

08/13/2008 3:26 PM

Be careful to choose calibration range. When you are measuring the cryogenic liquid you have to pressure the density based on possible pressure the tank is likely to operate. If saturation pressure varies so does the density and equivalent mmWC will change based on that

Register to Reply