cable size selection

06/22/2008 2:15 AM

How to select proper power cable size? i want to know that formula? and cable size selection chart according to KW/VOLT

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: cable size selection

06/22/2008 3:06 PM

Hello kumarnaik

This is a perennial question.

That means it keeps being asked repeatedly here at CR4 Forum.

Use the facility at right: "Search all of CR4", and enter the Search Terms.

Just to start you off, refer here: http://cr4.globalspec.com/thread/11833/power-cable-rating

I used the Search Terms: Cable Table

Trust that assists you.

If you need further help, reply here, with

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#2

Re: cable size selection

06/23/2008 4:22 AM

Use a larger cable than the code requires and you will not starve the eqwuipment for power causeing overheating and lowering the usefull life of the equipment.

__________________
If you never do anything you never have problems.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#9
In reply to #2

Re: cable size selection

06/23/2008 12:24 PM

This is accounted for by derating properly

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Anonymous Poster
#3

Re: cable size selection

06/23/2008 8:08 AM

Sizing a cable is a bit more complicated than simply looking at a table or pulling up a formula. You have to consider the environment the cable sees, you have to consider the load characteristics, motor? computer? Incandescent lamps?... Hire an electrician you cheap SOB and get it done right.

Register to Reply
Anonymous Poster
#4

Re: cable size selection

06/23/2008 9:25 AM

Simple answer! Get a copy of the American "National electric Code'' and it will simplfy your requirements especially since it considers temperature restriction of the type of insulation used.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: cable size selection

06/23/2008 11:05 AM

Please refer to the current edition of the Wiring Regulations, published and maintained by the IEEE.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#6

Re: cable size selection

06/23/2008 12:07 PM

There are numerous factors that need to be considered:

  1. Feeder or branch circuit (different multipliers for derating)
  2. ampacity required
  3. copper or aluminum
  4. ambient temp
  5. free air or in a raceway
  6. distance (to calculate voltage drop)

Yes, I'm a licensed Journeyman

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: cable size selection

06/23/2008 12:09 PM

I forgot. When all variables are calculated refer to Table 310 in the current Nat'l Elec. Code

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#8
In reply to #7

Re: cable size selection

06/23/2008 12:22 PM

Sorry wasn't logged in

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Anonymous Poster
#10

Re: cable size selection

06/23/2008 4:48 PM

When we select cable then we calculate these things.

1. Air temperature .

2. Load current ( how many load (current)on this Cable we used ).

3. cable capacity(all company allow cable maximum load capacity)

4. Voltage drop calculations:

5. Running voltage drop.

6. Distance (cable length)

7. cable laying ( under ground or open laying)

8. cable type ( 2 core , 3core,4 core).

these all things calculate then we laying a cable.

Note. All company give a chart where note cable maximun ampere capacity.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2008
Location: Bangalore
Posts: 8
#11
In reply to #10

Re: cable size selection

10/20/2008 12:33 PM

how to calulate voltage drop in cable?pls tel me the pormula

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#12
In reply to #11

Re: cable size selection

10/20/2008 7:53 PM

Hello again, kumarnaik

There is no single "Magic Formula", except Ohms Law, modified for the particular usage you intend..

There are many variables, as you have been advised above.

Consult the Maker of the cable you intend to use, and use that Maker's Cable charts for the actual type of cable you intend.

Those charts will advise you about deratings too.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); dadw5boys (1); kumarnaik (1); noshorts (2); PWSlack (1); Sparkstation (2)