Unstable Electrical Supply from Local Source (13kv)

07/02/2008 10:24 AM

I operate a factory in northern Mexico which has a problem each summer with electrical stability. The locals deny any instability in their grid but it is apparent that the problem is factory wide and not isolated to one of our 3 transformer fed areas. I want to know if there is a way I can monitor and record the electricity at any point, not necessarily the 13kv side, to prove the instability of the supply.

I am thinking of a PC based recorder or PLC based if anyone out there can provide a manufacturer I would be very grateful.

Register to Reply
Pathfinder Tags: electricity stability
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#1

Re: Unstable Electrical Supply from Local Source (13kv)

07/02/2008 11:40 AM

I used a full disclosure monitor made by Realiable (now part of Fluke). I rented it from an outfit by the name of Telogy. Check out the Fluke 1750 at http://www.telogyllc.com/application_details.aspx?applid=1

Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Unstable Electrical Supply from Local Source (13kv)

07/02/2008 1:38 PM

I would hire an electrical contractor. In that way you will have it in writing from an independent source. Will not be your word against the utility company.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2006
Location: Springfield, Tennessee U.S.A.
Posts: 231
Good Answers: 16
#5
In reply to #2

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 12:05 AM

I agree Ozzb. I'll bet that the problem is caused by the substation switching that is done to match demand, and the substation may not have suppressors installed on its switchgear. Also to consider-any close upstream or downstream users who move large switchgear. A professional power quality contractor is who is needed here, as he will seek the extremes of the span of the voltage and current levels, as well as seek out spikes and transients that can be very difficult to find without sophisticated recording equipment.

Best Regards,

Ing. Robert Forbus

__________________
"Yeah, but will it fit?"
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#3

Re: Unstable Electrical Supply from Local Source (13kv)

07/02/2008 10:22 PM

Hello Jeff in Mexico

If you use a local Electrical Contractor for the monitoring, it may be possible he is a friend or relative of a person in your Electricity Suppliers.

The best solution is to use an entirely independent Electrical Consultant or Engineer, with no 'ties' to the Electricity Supplier, or yourself.

That way, proper professional independence is maintained, and the report would thus be acceptable, hopefully to both parties.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Unstable Electrical Supply from Local Source (13kv)

07/02/2008 11:55 PM

Hi, i knew a company in india which manufactors Feeder monitoring system which logs allthe instantanious electrical parameters every 5 to 15 min intravals, stores the data for more then 10 years.

Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#6

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 12:15 AM

You may use Fluke 43-B for monitoring independent phases on low voltage side on 24 hours basis and thereafter take print-outs for further investigation by your internal distribution management team / by the utility company. Monitoring on low voltage side though has the uncertainty of internal Transformer malfunction attached to the analysis. This will however be applicable if you are using one transformer which feeds three factory areas and will not apply if you are using three transformers for three factory areas.

Regards

__________________
Karma is Dharma
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#7

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 1:14 AM

I use an Amprobe DM-II Pro (I think they are now up to the DM-IV). This is a three-phase monitor/recorder. I think they run on the order of $3000 or so...Variable recording periods, catches spikes and sags, rated up to 1000 V RMS.

Register to Reply
Commentator

Join Date: Mar 2006
Location: Sydney, Australia
Posts: 96
Good Answers: 5
#8

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 3:15 AM

I use the Socomex Diris A40 meter with the RS485 Jbus/Modbus module attached to the unit. This is then connected to a PC running software developed in Thailand. It has everything you need to monitor and log voltage, current, KVAr etc. Can also export to excel etc. Socomec has software but it's too expensive. Send me an email if you're interested and I will get you some prices.

__________________
Mark Taylor, Senior Technical Advisor, CV Bli Tek, Bali, Indonesia.
Register to Reply
Anonymous Poster
#9

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 6:31 AM

When I worked in industry, the standard for these measurements was Dranetz. Try Googling them.

Register to Reply
Power-User

Join Date: Oct 2007
Location: NW Ohio
Posts: 411
Good Answers: 25
#10

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 8:25 AM

You may be approaching the problem from the wrong direction. If you prove the instability with charts and reports you have now embarrased the local utility managers who probably don't have the authority or budget to fix the problem anyway. Utilities in Mexico have a way of being unstable and unreliable, but when confronted give shrugs and denials.

You would be ahead of the game researching how to resolve the problem for your factory. If you can clearly define the symptoms for this forum there are a lot of sharp cookies out there who can suggest solutions.

Been there, wiser for the experience.

__________________
Goodness has nothing to do with it.
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#11

Re: Unstable Electrical Supply from Local Source (13kv)

07/03/2008 11:42 AM

Electro Industries has a variety of high-quality digital meters for very reasonable cost. I've used their meters for nearly 20 years, and have never had a bad experience.

The Shark series meters have many options, including RS485, ethernet (wired or wireless), onboard data logging and power quality including THD. The best part is that you can order just the functions you need, without a lot of extra bells & whistles. If you later decide you need more options, you can upgrade in the field via simple software changes, without disconnecting the meter or even removing it from service.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Anonymous Poster
#12

Re: Unstable Electrical Supply from Local Source (13kv)

07/27/2008 12:01 AM

I would say that during the summer months demand is great and the LOAD TAP Changers are Maxed out on the Power Grid that you are fed from good luck trying to get those guys to address this.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); beriberi (1); chhotu1990 (1); cwarner7_11 (1); Ing. Robert Forbus (1); Lendog (1); ozzb (1); pwr2thepeople (1); Sparkstation (1); Tamu (1)