fault withstand level in switchboard

07/07/2008 11:35 PM

Why fault withstand level in switchboard has increased from 50 kA to 65 & 85 kA?

is it because of increase in rating of distribution transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: fault withstand level in switchboard

07/08/2008 12:03 AM

May be

1)The Z value of the transformer low

2)Transformer is nearer to the source

3) Transformers operating in parallel

Basically if the Impedance is low the fault current will be high then the switch boards has to be designed for to withstand the fault current for a specified time.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: fault withstand level in switchboard

07/08/2008 3:16 AM

Ther are some elements missing on your question, certainly the distribution system has been changed, transformer power and caracteristics and some users also addition of big motors?

Question shall be more precise.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: fault withstand level in switchboard

07/08/2008 3:33 AM

<...Question shall be more precise....>

The CR4 readership may well be looking forward to that state of affairs with excitement.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Apr 2007
Posts: 7
#4

Re: fault withstand level in switchboard

07/08/2008 11:18 PM

its actually, earlier customer was asking for 50 kA 1 sec in switchboard. now they ask for 85 kA 3 sec. what is the reason behind?

Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5
In reply to #4

Re: fault withstand level in switchboard

07/09/2008 12:27 AM

It seems there is drastic difference in fault level requirement.

May be the customer operating the transformers in parallel.You may request the customer to furnish details.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: fault withstand level in switchboard

07/09/2008 10:32 AM

If the customer is considering an increase in the size of the transformer, the fault current will go up.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#7
In reply to #6

Re: fault withstand level in switchboard

08/17/2008 7:29 PM

Size is not the main issue. A lowered impedance will allow greater fault currents for that brief moment when trouble occurs before the protection is activated. The rating states how much fault current the device or panel should be able to withstand momentarily without destructing. The impedence is affected mainly by sheer closeness of the supply transformer and by parallelling transformers to add available amperage. Also addition of capacitor banks can have a direct effect on the impedence.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); CJMcGill (1); potdarps (1); PWSlack (1); ramvinod (2); wareagle (1)

Previous in Forum: Light dimmer voltage?   Next in Forum: consultant

Advertisement