thermocouple cable

07/08/2008 8:51 PM

thermocouple cable, if the thermocouple cable come with screen wire, is't okey if i connected the screen on both end, one side connected to the junction box and the other side connected to FTA card. any problem will occur if connect both side?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: thermocouple cable

07/09/2008 3:20 AM

It is inadvisable in some circumstances to earth both ends of a cable screen. "Ground loops" can occur and cause distress. The phenomenon is most marked and best studied in analog audio microphone and gram pickup circuits, where "mains hum" can be a blessed nuisance and spoil the music.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: thermocouple cable

07/10/2008 9:18 AM

It is not recommended to connect a thermocouple screen wire to ground on both ends.

The industry best practise is to connect it to the instrument ground in the controller cabinet since you are assured of a healthy ground at the cabinet.

The ground in the field can corrode or become ineffective especially if the junction box is iro/metal and there is formation of oxides ( rust) etc.

As you may know ,thermocouple signals are in the order of very low level millivolts and any noise can result in unwanted results.

Register to Reply
Active Contributor

Join Date: May 2008
Posts: 12
#3

Re: thermocouple cable

07/12/2008 12:14 AM

Check if you have a grounded or ungrounded t/c if it is in a sheath