Testing Motor Repairs

07/11/2008 6:19 AM

i want to know that how many types of teste to be carried out after reparing / rewinding of 3-PHASE INDUCTION MOTOR -HT 6.6KV

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ht motor test

07/11/2008 7:35 AM

What does the Client's test specification say? Presumably someone will be there to witness them!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#5
In reply to #1

Re: ht motor test

07/14/2008 1:38 AM

I WANT TO KNOW METHOD FOR CORE FULX LOOP TEST FOR 3-PHASE A/C INDUCTION HT MOTOR 6.6KV .

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Testing Motor Repairs

07/12/2008 9:26 AM

First of all check what facility the rewinder has to offer for testing.strictly speaking if I were the client I would do all rotine test as per IEC/BS and also a temp rise test which is not possible in many of the rewinder's shop.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#3

Re: Testing Motor Repairs

07/12/2008 11:40 AM

Minimum:

  • Insulation with a HV megger first.
  • Winding resistance, check for symmetrical values in all three phases.
  • Be sure all protections are set accordingly to the motor nameplate rated values.
  • No load run - observe vibrations
  • Run under increasing load, if it is possible - measure V, I, P, Q

IEEE, NEMA, ISA materials could help.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#6
In reply to #3

Re: Testing Motor Repairs

07/14/2008 1:47 AM

CAN IU GIVE A CORRECT METHOD FOR MEASURING OF CORE FLUX LOOP TEST(HOT SPOT) FOR HT MOTOR IN DETAILS ?

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 11
Good Answers: 1
#4

Re: Testing Motor Repairs

07/13/2008 4:21 AM

A Megger test is the most important test to be carried out. I would suggest a saturation test at 10KV for about 20 min.

You can also test run the motor on 415 Volts (or whatever your equivalent). This will allow a longer timeframe to achieve full speed which will allow for more in depth current balance testing.

Register to Reply Score 1 for Good Answer
2
Participant

Join Date: Jul 2008
Posts: 1
Good Answers: 1
#7

Re: Testing Motor Repairs

07/23/2008 7:59 AM

I run an electric motor rewind shop and to answer your question correctly, I would need you to answer a question for me. Are you looking to test the electrical functionality/integrity of the motor or the mechanical functionality or both?

There are quite a few different ways to test the electrical integrity of a motor. Most tests are done before the work is done to determine the scope of work needed to bring the motor back to full capability. The two most important tests are the meggar and the surge test. Megging the motor will look for shorts from phase to ground, while surge testing will compare phase to phase and likely catch turn to turn faults. You can combine this with hi pot tests( possibly destructive if not done correctly) and of course a good visual of the stator, laminations, windings, end strings.

Motors that have experienced any type of damage to the lamination stack(rotor dragging on stator, ground short in the slot) must be core loss tested to determine if any hot spots will be present and how much efficiency will be lost. Some of the problems can be rectified. A bar to bar test can also be performed to test the integrity of the rotor. An open bar in the rotor can also be detected via vibrational analsis.

Mechanical damage to rotor journals, bearing housings, laminations, and balancing of the rotor must all be rectified at the time of the rewind

After the motor is rewound and all mechanical work performed it can be assembled and further tested. A full dyno load test can be performed and balanced three phase load. In addition, megging and surging the motor again can be performed again to further validate the work performed. It is also a good idea to perform vibrational analysis when dyno load testing to check vibration levels.

Of course all this work is not usually carried out on smaller motors due the point of diminishing returns, but on larger motors any and all testing must be thoroughly performed. the latest on the technology front for motor testing is MCA(motor circuit analysis) which can test air gap eccentricity among other things which i am not very familiar with, yet.

Register to Reply Good Answer (Score 2)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); nesubra (1); PWSlack (1); ray.l (1); Rockey (1); southern123 (1)