Panelview to PLC-5

07/11/2008 9:13 AM

Hello, I am having problems getting a panelview to display receiving displayable outputs from the PLC-5/60, I assume a connection issue is likely the problem, I was wondering how you setup the PLC-5/60 to connect to a panelview, I.E. do you have to use RSLINX or whatnot, thanks to anyone who could help me out with this.

Regards,

Eengineer21

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Jun 2008
Posts: 9
#1

Re: Panelview to PLC-5

07/11/2008 9:34 AM

Sorry, there is a change to the above statement, it is a panelmate not a panelview. Thank you.

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Panelview to PLC-5

07/12/2008 6:07 AM

I've used Panelview but never used Panelmate so I can't help you with that particular bit. I'm going to make a guess and take a shot at it.

Basically, to get your PLC and display talking to each other, you need to get them talking at the same rate. You'll need to set the baud rate or speed to be the same for each of them.

Next, you need to define what you're using to communicate. Is it DH+? Remote I/O?, Ethernet, etc.

Then you need to tell the Panelmate the address of the PLC that it needs to get data from.

Hardware-wise, if it's just the PLC and the Panelmate (assuming it's Remote I/O), you'll need terminating resistors at both ends. I think the PLC has one built-in but you'll have to set a DIP switch to put it in. If you have several devices connected together, you'll need to put the resistor at the two ends of the line. I can't remember the exact value of the resistor though. It should be in the manual.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2007
Location: The wilderness of NH - USA
Posts: 19
#3
In reply to #2

Re: Panelview to PLC-5

07/12/2008 7:22 AM

What you can use for resistor for 57.6k baud rate is 150 Ohm and 243k baud is 82 ohm. Termination is required for both ends of the Dh+ and Remote I/O.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2007
Location: The wilderness of NH - USA
Posts: 19
#5
In reply to #3

Re: Panelview to PLC-5

07/14/2008 1:59 PM

There is correction to the Baud rate of 243, should have been 234k Baud and 82 Ohm resistor for termination at both ends. sorry for the confusion.

Register to Reply
Member

Join Date: Jun 2008
Posts: 9
#4

Re: Panelview to PLC-5

07/14/2008 8:24 AM

Thank you very much, hopefully we will be able to get it setup. I'll try changing the baud rates to get them to match. Thanks.

Register to Reply