What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/14/2008 5:12 PM

In hand specification for slab thickness 10 cm on grade for a factory where l maximum load is a machine whit 10 ton weight and 8*0.7 meter size.

Procedures: Gravel layer 10 cm, sand layer 5 cm, leveling, water adding, compacting 11 ton wake behind roller, nylon sheet 500 gram, cartoon for expansion joint 2.5*2.5 meter slab, chair for rising steel mesh up, steel wire mesh 8 mm, concrete 350kg /m3, concrete fan leveling, concrete surface hardener.

In fact these procedures are costly, I am looking for cheaper way even with little headachy in future.

Cheers

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#1

Re: What is the final word for rebar conc slab on grade, steel structure mrzzanine?

07/14/2008 11:37 PM

Well why don't you just use a gravel pad? That is a whole lot cheaper. If the ten ton weight sinks into the soil...no big deal...stick a couple of railway ties under it and Bob's your uncle! It is really a pleasure dealing with a big time spender like you! Hope your headachy is not too painful!

__________________
Bruce
Reply Good Answer (Score 3)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2
In reply to #1

Re: What is the final word for rebar conc slab on grade, steel structure mrzzanine?

07/15/2008 4:38 AM

Hello ba/ael

from me

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Reply Off Topic (Score 5)
Power-User

Join Date: Jan 2007
Location: The Capital City, Cow Hampshire, USA
Posts: 476
Good Answers: 3
#3
In reply to #1

Re: What is the final word for rebar conc slab on grade, steel structure mrzzanine?

07/16/2008 7:08 AM

Rest assured: Any 1st cost savings will be repaid @ 10 000% w/ later headaches.

DON'T BE "CHEAP", be frugal.

__________________
If you always do what you've always done, You'll always get what you've always had!
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Mining Engineering - New Member Engineering Fields - Construction Engineering - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Scottsdale, AZ
Posts: 1014
Good Answers: 12
#4

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/16/2008 7:40 AM

Why are you compacting the aggregate, added the sand for chinking and the vapor barrier all this will do is trap water under causing you trouble down the road? Why only 10 cm of concrete? It should be at least 15.25 cm to support the weight.

My suggestion 15.25 cm-20.33cm of 2.5 cm aggregate (un-compacted) with the wire mesh on rockers with at least 15.25 cm concrete Class AA (ACI).

__________________
John J Baker
Reply
Power-User

Join Date: Jan 2007
Location: The Capital City, Cow Hampshire, USA
Posts: 476
Good Answers: 3
#5
In reply to #4

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/16/2008 7:50 AM

My take in original query is that it is an 'inside a building' floor, will be used as a foundation for 'some sort of UNDEFINED machine tool'.

The compaction steps i'd consider mandatory, to prevent settling later. The vapor barrier would be to prevent moisture from infiltrating into the shop space (rusting, &al)

In the overall scheme of things preparation & concrete are small costs; overbuild! Tomorrow you WILL need more.

__________________
If you always do what you've always done, You'll always get what you've always had!
Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Mining Engineering - New Member Engineering Fields - Construction Engineering - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Scottsdale, AZ
Posts: 1014
Good Answers: 12
#6
In reply to #5

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/16/2008 8:15 AM

If they are using the floor then why the aggregate? Why not drive rebar rods into the floor apply concrete epoxy add your 3 1/2 inches of concrete with wire mesh and be done with it.

Compaction and the sand chinking will not allow any water to pass through causing buckling. The vapor barrier will cause a whole host of issues with the concrete itself from stress or reflective cracking to not allowing the concrete to completely dry.

What they are asking for isn't over engineering it's called asking for trouble. If you want to over-engineer do what I suggested before with the 6 inches of 1" aggregate and 6 to 8 inches of class AA concrete with wire mesh then if you want add fiberglass fibers.

__________________
John J Baker
Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Mining Engineering - New Member Engineering Fields - Construction Engineering - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Scottsdale, AZ
Posts: 1014
Good Answers: 12
#8
In reply to #6

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/16/2008 9:23 AM

What's off topic? I guess getting an opinion from someone who's done this kind of work for 14 years is to much for some people.

__________________
John J Baker
Reply
Guru

Join Date: Nov 2007
Location: Sherwood Park, Alberta, Canada
Posts: 1212
Good Answers: 74
#9
In reply to #6

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/17/2008 12:27 AM

This sounds like a load of rubbish to me! What exactly are you saying? Does it not depend on the subgrade modulus? Are you suggesting that your solution is good for all soil conditions? If not, then why don't you qualify your answer? I don't believe you know what the heck you are talking about!

__________________
Bruce
Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Engineering Fields - Mining Engineering - New Member Engineering Fields - Construction Engineering - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Scottsdale, AZ
Posts: 1014
Good Answers: 12
#13
In reply to #9

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/18/2008 8:23 AM

Coming from someone who wants to put down a gravel pit and railroad ties I will take this a a complement.

I guarantee that what ever industrial equipment he puts down isn't going to move it you put on 6 inches of 1" stone and 6-8 inches of concrete with wire and fiber. It's a common practice over here in PA for road construction or other industrial sites, plus PA has a wide varied of soil times. If this is to be placed on a concrete floor you can easily tie it in by drilling in rebar apply an epoxy that will allow the old concrete to adhere to the new concrete add you wire mesh and fibers and your set. If they want to rip up the old concrete flooring and lay down a new section soil what be an issue because the area is pretty much compacted from before add you stone and concrete as stated above and away you go.

__________________
John J Baker
Reply
Power-User

Join Date: Jun 2007
Posts: 183
Good Answers: 3
#7

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/16/2008 8:28 AM

10 cm or 4" thick slab seems very thin for a factory. That's the thickness of a sidewalk! The waking sounds like a vibratory roller. That would be a big mistake on some soils. 4" of stone is usually good, but the choking with sand is used to "tightenup" the base. If the soils underneath are bad enough that you need more strength from the stone base make it thicker. It probably the manpower that is the most costly part. Besides all that, the vapor barrier is now full of holes from "whacking" it with all of that sharp stone.

Since you are using a walk behind roller, this suggests to me that you are working in a confined space such as under a roof. if you used a finer stone such as #8, 0r #9 (pea size gravel) you would not need to compact it. Also the chairs for the rebar is a good thing, but most of the time the concrete guys step on it and press it to the bottom where it does no good. They hate using it.

If I were doing this I might (depending on the geotechnical engineer's recommendations), use the following:

compacted subgrade, 4" (10 cm) of #8 stone, vapor barrier, 5" of 4000 psi concrete with fiber reinforcement and not rebar/ mesh.

Reply
Anonymous Poster
#10

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mezzanine?

07/17/2008 8:09 AM

Dear all

Thanks for your valuable time, Please read below and comment?

http://www.cement.org/tech/faq_fibers.asp

Reply
Anonymous Poster
#11

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mezzanine?

07/17/2008 8:16 AM

Below is what in http://www.cement.org/tech/faq_fibers.asp for your quick review

Frequently Asked Questions
Cement & Concrete Technology Home > FAQs > Fibers

Q: Can fibers replace wire mesh or welded wire fabric in a concrete slab on ground?

A: To answer this question, it is first necessary to establish why wire mesh or fibers would be used in a concrete slab. One of the main reasons is for crack control. PCA, however, states that cracks in slabs on ground can be controlled with uniform subgrade support and proper joint spacing (as a function of slab thickness). See Table 6-3 from PCA's Concrete Floors on Ground (EB075).

Table 6-3. Reinforcement for Floors on Ground

Is reinforcement necessary?
NOWith uniform support and short joint spacing
YESWhen long joint spacing is required
When joints are unacceptable in floor use

Although short joint spacings alleviate the need for reinforcement, wire mesh will allow for increased distance between joints if correctly placed in the upper portion of the slab, at least 2 in. below the surface. In these slabs with longer joint spacings, the purpose of wire mesh is to hold random intermediate cracks tight.

Plastic fibers should not be expected to replace wire mesh in a slab on ground. However, although not affecting joint spacing, plastic fibers are used to reduce plastic shrinkage cracking.

Plastic shrinkage cracks are those that occur immediately following concrete placement, before the concrete has hardened. Plastic fibers are commonly dosed at 0.1% by volume for slabs on grade; this is equivalent to 0.9 kg/m3 (1.5 lb/yd3). Polypropylene fibers are among the most common for controlling plastic shrinkage cracking. There are many types of fibers in addition to polypropylene, including other plastic materials, such as nylon. Fibers serve different purposes based on the characteristics of the material from which they are made. For instance, steel fibers provide high flexural strengths and impact resistance and are found in heavy-duty industrial floors.

For additional information on fibers for use in concrete, see Fibers(IS532) and Fiber Reinforced Concrete (SP039)

Reply
Anonymous Poster
#12

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/17/2008 8:28 AM

I need more infromation about wire mesh on rocker

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#14

Re: What is the Final Word for Rebar Conc Slab on Grade, Steel Structure Mrzzanine?

07/24/2008 1:56 PM

10 cm, that is like 4 inches. 10 cm is nothing, someplaces end up with 10 feet of aggregate base rock underneath and entire facility. This is thinner than many commercial concrete driveways (about like a residential driveway or sidewalk with reinforcement, except the aggregate thickness is a little thin). The cost of materials is probably about as cheap as you are going to get for any marginally effective support. Though i guess you could do just about anything if you were willing to pay the repairs to maintain the equipment within balance and alignment requirements every so often. How much would it cost you to take this 10 ton equipment off line for a few days and move it to do repairs every few weeks or so?

Reply
Reply to Forum Thread 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); ba/ael (2); bakerjohn (4); jrpeck (1); RCE (1); sidevalveguru (2); Sparkstation (1)