current carrying capacity (can u solve this)

07/16/2008 12:28 PM

tell me how can I find size of aluminium conductor

rating-3000kw

voltage-420v

current-5155A

3 phase

pf-0.8

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: current carrying capacity (can u solve this)

07/16/2008 7:16 PM

Take a look at the table listed at this site.

http://www.houwire.com/products/technical/article310_16.html

You need about

17 ckts in separate conduits of 500 kcm al which I think is ridiculous. You need to make some changes in the design. Maybe higher voltage.

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: May 2008
Location: Placerville, CA
Posts: 80
Good Answers: 8
#2

Re: current carrying capacity (can u solve this)

07/17/2008 12:00 AM

A little information about your application would be helpful.

Typically, this amount of current is only seen at generator terminals and is handled by solid bus.

As stated by wareagle, you may need to rethink the design of your system. A couple of transformers could be in order.

__________________
ALL "electrical" failures are mechanical in nature.
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: current carrying capacity (can u solve this)

07/17/2008 3:01 AM

As implied by earlier posts, 3 Megawatts at 420 volt system is not a practical instalation. Even if you could find suitable cable, your connections to the device would be unwieldy and the internal conductors and terminations would not be feasible.

Are the numbers correct? Power in those quantities is typical of power generation equipment or maybe extremenly large mining equipment (like draglines) that would normally run much higher voltage.

I helped install a complete switchyard for a coal mine and that only handled 100 Amp per phase on 11000 Volt.

Power losses in the conductors at your proposed current of 5155 Amp would represent significant expense and pose additional challenges for your system in maintaining it's own stability and not melting away.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: current carrying capacity (can u solve this)

07/17/2008 9:08 AM

Consult an appropriately-qualified Electrical Engineer!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Just an Engineer (1); Mark684 (1); PWSlack (1); wareagle (1)

Previous in Forum: Inverter problems   Next in Forum: Copper vs aluminum wiring

Advertisement