Light circuit tripping when turning off

07/18/2008 12:08 AM

Part of our history is that we bought a relocatable school building, moved it to the farm and converted it into a house. The original circuits were replaced and upgraded from fuses to RCDs along with necessary meters and so on.

All the original lighting in the house is twin tube flourescent lighting battens.

The problem is that occasionally, the RCD trips when the lights are turned off. Never happens at turn on, never happens during normal "on" time. The trips are not isolated to an individual room switch. (Two completely new (also fluorescent) light sets in the house have not shown this fault but are on same supply circuit.)

I have a theory and am looking for confirmation before going further down the track.

My hypothesis is that the old ballasts are "dumping" energy in the turn off process and this is causing the RCD to sense a current imballance and trip.

Is that a feasible cause of this symptom?

If so, then how can I legitimately make it go away?

(Location is Australia, non-city, grid connected.)

Thanks in advance for all the wonderful advice that I know will come.

__________________
Just an Engineer from the land down under.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#1

Re: Light circuit tripping when turning off

07/18/2008 1:35 AM

I had more or less the same problem and I suspected the ballast as well.

I replaced the suspect light fitting but also checked all the earth and other connections in the stove. (also high on the suspect list)

I don't know what solved the problem but it is OK now.

By the way I posted a picture of the patterns caused by the ballast on CR4 and was told that it is those 38 year olds are not used any more. (why the patterns?)

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Anonymous Poster
#2

Re: Light circuit tripping when turning off

07/19/2008 12:17 PM

It's possible that you had a three-way switch that was reconnected wrong or replaced by a regular switch but had the same wiring - since it sounds like you had some upgrades - then when you turn it off it's shorting.

Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#3

Re: Light circuit tripping when turning off

07/21/2008 4:31 AM

Check whether power factor correction capacitors are fitted in the suspect lights, possibly the new lights have them and the old ones don't.

Register to Reply
Power-User
United States - Member - Member

Join Date: Dec 2006
Location: La Grande, Oregon U.S.A.
Posts: 468
Good Answers: 23
#4

Re: Light circuit tripping when turning off

07/21/2008 4:59 PM

Just,

I would like to sound an alarm bell here. I recently smelled wood smoke when leaving work in the evening. I checked around and found an old ballast that was quietly cooking off, and starting to burn the wall. Some of those old devices lacked adequate thermal protection and would start fires. If you are having any questionable behavior in the old fluorescents - beware and replace.

LG_DAVE

__________________
Don't hit at all if it is honorably possible to avoid hitting; but never hit soft! - Theodore Roosevelt
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#5

Re: Light circuit tripping when turning off

07/21/2008 5:50 PM

Thanks all for your input so far.

I can confirm that there are power factor correction caps in all the fittings (Checked this when we moved the building) but we did not "measure" them as at the time there was no reason to suspect anything like this.

I can also confirm that they are only getting warm (not hot) as per normal expected performance. At my work in the last few months we also had a flourescent balast cook itself. Evacuated 400 people and took an hour for the "all clear" to return.

At home, we have been plotting a scattergram of the lighting condition each time the circuit trips. (Which ones were on, which one was switched and so on.) Ironically, it seems more related to environmental conditions than anything else. Seems to happen after 5pm until around 1am when there is potential condensing atmosphere. Doesn't happen in the mornings when getting ready for work/school and so on (5am till 8.30am)

I'm now thinking of progressively replacing the light sets in some parts of the house and in the others there are now available LED replacement devices for flourescent tubes that I might give a try. (eliminates balast and capacitors from the circuits.)

Might even prototype some lamps at work. (We manufactur LED lamps amongst other things and there are the right resources there to do this properly.) Who knows, if they work well, we might start to manufacture them for general sale.

Any additional thoughts are still welcome.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#6
In reply to #5

Re: Light circuit tripping when turning off

07/21/2008 6:38 PM

Are the fluorescent fixtures grounded?

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#7
In reply to #6

Re: Light circuit tripping when turning off

07/21/2008 7:12 PM

The light fittings are definately grounded as follows.

The supply circuit has active, neutral and earth and the earth is connected to the fitting. The building frame is also welded steel construction and the fittings are screw attached to that framing.

The meter box has the mandatory ground connection to a 12mm stake that is 2m into damp clay and the building frame has 28 x 18mm diameter steel (cyclone tie down fastening welded to the frame) bolts that each extend 1m into 2m deep concrete footings.

The water supply pipe for the house is also bare copper attached at more than 25 locations along the length of the steel building. That pipe extends more than 6m underground and would also provide some level of ground potential connection.

From the above observations I presume that the fittings are grounded and that the grounding is effective.

As an asside, the tie down straps paid for themselves in the first year after we moved in. There was a little storm that came through. Insurance estimates wind speed was around 200kph, it made a mess, but the house (generally) remained intact. (A couple of windows broke, furntiture moved around inside, floor coverings stripped and dumped in the hallway, lots of scared people) but that's another story.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#8

Re: Light circuit tripping when turning off

07/23/2008 6:13 AM

If/when you replace those ballasts, check each of them for a sticker that says there are "no PCBs" contained. If there are no such stickers (old ballasts had PCBs), please dispose of them properly (not in ordinary trash). Don't know what the exact OZ rules are, but they are a health hazard.

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#9
In reply to #8

Re: Light circuit tripping when turning off

07/23/2008 5:32 PM

Thanks for the reminder. I am fortunate in that where I work has contracted hazardous waste disposal contracts and our employer encourages "environmental responsibility" for the employees inclusing allowing us to put that sort of stuff into our hazardous goods waste (identified) for proper disposal.

I don't remember seeing any of those stickers on the ones that have been opened for inspection or fitment, so it seems that I'll eventually have 21 of them to dispose of.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#10
In reply to #9

Re: Light circuit tripping when turning off

07/23/2008 5:42 PM

Suspicions confirmed - happy to be of service, sah! Good on your employer, you may quote me on that.

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Chankley (1); cwarner7_11 (1); EnviroMan (2); Hendrik (1); Just an Engineer (3); LG_Dave (1)

Previous in Forum: Just a Theory   Next in Forum: Practice vs Perform
You might be interested in: Ballasts, Lighting Controls, Lighting Design Services

Advertisement