My question is for those who is familiar with ETAP Power Station (Ver. 4.0.0). I am trying to carry out the load flow calculation in ETAP Power Station 4.0.0. However this module fails to perform, permanently giving the following error messages:
Error 2000: Number of energized buses is less than two.
Error 2001: The system has no swing power grid or generators.
Error 2002: The system has no energized branches.
I tried even the simplest system (generator, cable, bus and load) but without any result.
Is it software error or is there anything to be changed in configuration and/or in parameters ?
Your help or suggestions will be highly appreciated.
Paata
Re: ETAP Power Station
07/20/2008 3:54 AM
You should first check if you really did it right (e.g. You have energized buses, swing power grid, etc). If nothing happens, contact the service/maintenance section of your ETAP supplier. They should be able to help.
Gemini EE
Good Answers: 19
07/20/2008 6:40 AM
There is nothing wrong with the software.I am familiar with the usage.
You have to properly configure and select the buses and source etc.
Ramesh,Freelance Electrical/automation Consultant
07/20/2008 2:02 PM
No energized busses implies that you have not configured the source of power properly. You must have at least one power source configured as a swing bus (loadflow calcs always need a swing bus to 'take up the slack'). Secondly there must be more than 2 buses for the loadflow to execute so add more system elements.
07/21/2008 2:02 PM
Thanks for comments
As per your recommendation I managed to decrease error messages to one: "Error 2002: [project1] The system has no energized branches" by applying swing mode for generators. Question: what parameter should I change in branches (e.g. cable) table to eliminate Error 2002 and carry out the load flow, since I tried to use more than two busses without any result.
Thanks in advance
Paata
Good Answers: 19
07/21/2008 10:27 PM
Have you closed the breakers/switches for the power to flow?
07/22/2008 8:31 AM
Mr Ramvinod don't beat in the bush. I will suggest Mr Paata to first get familier with ETAP. Read manual, help files and sample models. Hope you will solve your problem. I have worked quite a no of projects on ETAP, the errors you are saying is nothing but your ignorance.
BNDas
07/22/2008 10:12 AM
I would like to particularly thank you Mr. BNDas for your valuable help
Now I will know that there is "Help" capabilities in the software and manual as well.
07/22/2008 10:03 AM
Hi
I don't have problem with load flow any more. What I did was to add fiew more elements to the system and result was satisfactory. I hope there shouldn't be any problems with more complex systems.
Thanks for support
02/03/2010 8:32 AM
Try adding cable in-between DG & your MCC.
Jassen.
03/15/2010 3:58 AM
Hi Paata,
Can you share with me what is the new elements havu you added in to solve this problem? I'm currently facing the same problem like you.
Amrul
03/29/2010 9:54 AM
If you are using Etap version 4.0 these days, I'd say you were onto a pirate version.
No wonder you didnt call the supplier!
nmo
03/29/2010 9:57 AM
Amrul I suggest a transformer and a bus, with no load on it.
nmo