Cable Size

07/19/2008 4:49 PM

How to calculate the size of the cable for the load 1000 kW and the distance is 245m? Is it possible the 1000KVA trans will take the load or need another Transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: Cable Size

07/19/2008 7:01 PM

A little more information is required before any meaningful answer can be given to the first question. Voltage and type of supply system (DC, AC single phase, AC 3-phase) would seem like a good start. Desired cable material (copper, aluminium)?

As to your second question, it depends on the type of load, but probably you will need more transformer capacity to supply 1000KW. If the load was purely resistive, and if you didn't mind running the transformer at 100%, the you might just get away with this transformer alone, but is this a good idea?

__________________
paulusgnome
Register to Reply
Participant

Join Date: Jul 2008
Location: Saudi Arabia
Posts: 3
#5
In reply to #1

Re: Cable Size

07/20/2008 4:09 PM

We are setting up a new block factory for that I have to calculate the cable size. The details are ----

Voltage = 380v AC 3phase

maximmum load = 585 kW minimum = 535 kW ( Block Plant )

load = 415 kW for future facillity

Available Transformer = 1000KVA We have requested another Transfomer of same capacity

As mentioned earlier the distance is 245 m and desired cable material - copper

Help me !!!!!!!!

If anyone know the website for free online calculators it will be great...........

Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#7
In reply to #5

Re: Cable Size

07/21/2008 9:27 AM

380/220 V, 50 Hz system is EU standard so if you do not have your country tables, maybe German or UK would be available. US _ NEC tables for Cu can be used for comparison. The supplier (your source for buying cables) should have also tables for cable ampacity. Be sure to apply all factors (temperature etc.) in multiplication.

I apologize for errors in my first post.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Cable Size

07/19/2008 11:29 PM

As Paul said you need to post more information. I am interested in your background.

This is a simple problem for anyone with sufficient experience in the electrical field.

Do you have any experience?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Cable Size

07/20/2008 6:46 AM

1000 kVA trafo will not be suitable for your load of 1000kW.Assuming the pf of the load is 0.8 ,kVA rating required will be 1250 kVA further you have to consider other aspects,in my opinion you may have to go in for 1500 kVA trafo.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#4

Re: Cable Size

07/20/2008 11:32 AM

All extra questions necessary to select (a) transformer, (b) cable are essential.

About the load it is also v. important to know:

_ Its fluctuation in time. E.g. if 1000 kW is just a 15 minute peak and the rest of the time (say in 24 hrs) is 600 kW, 1000 kVA transformer would be OK.

_ The temperature at the time of peak demand.

_ The type of transformer cooling system: AIR, OIL or OTHER. As well as its overload protection.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Cable Size

07/21/2008 6:59 AM

<...to calculate the size of the cable for the load 1000 kW and the distance is 245m...>

It depends upon a lot of factors, including the country codes. In the UK it is covered by the latest edition of the Wiring Regulations, published by the IET.

http://en.wikipedia.org/wiki/Electrical_wiring

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Arif (1); Paulusgnome (1); PWSlack (1); ramvinod (1); southern123 (2); wareagle (1)