iiee Correction factors for cable size com.

08/04/2008 3:51 AM

What is the correction factors (IIEE standards)applied for Computation of Cable size?

__________________
No one is an island....
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: iiee Correction factors for cable size com.

08/04/2008 4:32 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#2

Re: iiee Correction factors for cable size com.

08/04/2008 9:21 AM

We use NEC (National Electrical Code) in the US as a standard. I am not familiar with IIEE. There are publications by IEEE (Institute of Electrical and Electronic Engineers) in the US regarding cable size and current-carrying capacity (here referred to as "ampacity").

Cable size with regard to ampacity is rather complex. It is a thermodynamic system and there are several variations of installations. Most code books rate single conductors in free air, no more than 3 conductors in conduit, etc. Then there are tables to de-rate for more than 3 conductors, higher ambient temperatures, etc.

Hope you find what you're looking for.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Member

Join Date: Aug 2008
Location: Dubai, U.A.E.
Posts: 6
#3

Re: iiee Correction factors for cable size com.

08/05/2008 1:37 AM

We use NEC (National Electrical Code) in the US as a standard. I am not familiar with IIEE. There are publications by IEEE (Institute of Electrical and Electronic Engineers) in the US regarding cable size and current-carrying capacity (here referred to as "ampacity").

Cable size with regard to ampacity is rather complex. It is a thermodynamic system and there are several variations of installations. Most code books rate single conductors in free air, no more than 3 conductors in conduit, etc. Then there are tables to de-rate for more than 3 conductors, higher ambient temperatures, etc.

Hope you find what you're looking for.

Thanks but if its ok to you an you still send me the table for derating more than three conductors cause here in dubai the authority had guidelines here in computing cable sizes and according to my analyzation their having 1:2 ratio for KW:A (rating of MCCB) on main feeders etc. the max ambient air temperature here was 48-52 deg. and using an electricity supply voltage of 230/400V ±10%,50Hz,3phae 4wire and seperate neutral protective con.) and can you tell me if theres any difference in british and us standards accoeding to electrical codes.

__________________
No one is an island....
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#5
In reply to #3

Re: iiee Correction factors for cable size com.

08/12/2008 10:47 AM

May I refer you to this chart and others: Okonite web page showing NEC table, and this page by PowerStream showing charts, calculators for voltage drop, etc.

What you need is available on the world-wide web, so Google it.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#4

Re: iiee Correction factors for cable size com.

08/09/2008 12:46 PM

You can find the answer here: http://www.electricsmarts.com/ Check my blog for other e-learining sites: http://philipjarina.blogspot.com/

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (2); michaelbillones (1); PWSlack (1)

Previous in Forum: Reel to Reel Tape to Computer Interface   Next in Forum: motor
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement