We are using anubar as a primary element in flow measurements in my plant...
Maximum Flow : 170000 NM3/Hr.
Media Temp.: 260 Deg.
Design DP : 676 mmWc
Media Temperature:
Media: Hot n clean air
Secondary Instrumentation: DP Transmitter
Problem:
Not getting proper flow.
Analysis:
Maximum Flow at Maximum (676pa) DP: 170000 NM3/Hr
Transmitter scale: 0 - 1000Pa
PLC scale: 0 - 1000pa
We are unable to justify the doubts by operation departments. Will u any one can please send your openion.
Thanks & Regards,
Good Answers: 54
Re: using flow transmitter
08/14/2008 8:41 AM
Your info has a discrepancy.
mmWC (millimeters water column) is not equal to Pa (Pascals). Also remember that mmWC is referenced to 4°C, not 260°C.
08/27/2008 12:02 PM
Pls check if any leakage is there in the drain valve.
08/14/2008 11:37 AM
flowrate = square root (DP) *6538
SO: 676^.5 * 6538= 170000
Good Answers: 54
08/14/2008 11:09 PM
What unit are you using? mmWC or Pa?
08/16/2008 1:41 AM
Dear Guest
Ref to attcahed file , Kindly Check Your DP range Since the mentioned formula as such is very basic and is not used for annubar sizing, you can convert Your flow into standard condition and size for Dp Based on the selected model "K" and the flowing Pressure and Temp ,( or Select K =0.6),and then recalibrate Xr
Also verify upstream conditions are met, manufactuer will be able to provide the up/down stream requiremnets.
For more Info Visit Dietrich Emerson
Regards
Jose
01/05/2025 5:19 AM
Discuss with the equipment vendor directly. Telephone?
Good Answers: 54
01/13/2025 11:50 PM
This question is 17 years old and he never answered my question about the units.
He mentioned his instrument is set for 676 mmWC (or 676 mmH2O). Then, he mentions that his maximum flow is set at 676 Pa. Then, his transmitter and his PLC are both scaled for 0 - 1000 Pa.
According to my conversion app, 676 mmH2O is 6629 Pa. So, no wonder his instrument is not giving correct outputs.
I hope he's solved his problems (even after 17 years) (",)