Wiring a Transformer

08/20/2008 9:26 PM

I have a 112 KVA Delta 3-phase to a WYE 208 Transformer that I want to use for a 100 Amp Breaker Panel only. I know this over-kill but it was free. This is probally be the only thing on it. But, I would like to know if I can use a smaller wire like a number 8 wire for the 480 primary side and a number 2 wire for the 100 amp panel? Even though I am only using 1/4 of this would this be acceptable? Please someone let me know!

Thanks Gary

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Transformer

08/20/2008 11:35 PM

Your wiring size must be rated for carrying at least the rating of the protective device protecting it (in this case a 100A circuit breaker).

I am assuming that you know what wiring size you need that will be able to handle 100A in your particular application, if not see previous threads on wiring size selection.

__________________
jack of all trades
Register to Reply Good Answer (Score 4)
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#2
In reply to #1

Re: Transformer

08/21/2008 3:57 AM

Hello jack of all trades

from me

Kind Regards (from the Mainland)....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
4
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Wiring a Transformer

08/21/2008 10:14 PM

The minimum ampacity of the secondary conductors is a product of the primary side over current device.

The ratio of the secondary to the primary on this transformer is 480/208 or 2.30:1. So to limit the secondary current to 100 amps, the primary needs to be fused at, using the equation of 100/2.30, 43 amps. I would use a 40 amp breaker to protect the primary and #8 AWG wire. Or you could use a 50 amp breaker, with #6 feeding the transformer, and still be within the ampacity limit of your #2 on the secondary.

If you wanted to use the full 112kVA... you would need the following...

Primary max amps = 134.9 A

Secondary max amps = 311.2 A

Max Standard Primary Overcurrent device = 175 A

Minimum Primary Conductor Ampacity = 168.6 A

Minimum Secondary Conductor Ampacity = 389 A

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 4)
Participant

Join Date: Aug 2008
Posts: 4
#4
In reply to #3

Re: Wiring a Transformer

08/22/2008 7:30 PM

Yes! This is what I came up with on the fuses and the wiring. I know this is a over-kill Transformer but it was free. I might run heavier wire and run more panels at another time if I ever need them. Thanks for your answer.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Wiring a Transformer

08/22/2008 10:31 PM

Now... check your local codes and see if that approach is acceptable. Your local regs might require you to provision the transformer with what it needs to supply the full 112kVA. Not likely... but possible.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#6
In reply to #3

Re: Wiring a Transformer

08/24/2008 11:10 PM

Hello North of 60

from me

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Off Topic (Score 5)
Register to Reply 6 comments