I am in Angola in a place which have a lot of power cuts, we switch from mains to gensets and backwards, I have a lot of frequency drives blown in the 380V side, I already have a UPS and a Voltage regulator. Who can help me to solve the problem?
Re: Problems with Danfoss Drives
08/22/2008 10:37 AM
The generator set supplier and the drive manufacturer should be at the top of the list.
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
08/22/2008 11:00 PM
Hi.. I can help you zero-down on the root-cause of the problem. Can I have the single-line diagram of the power-flow in your facility right from Utility point to Drive.
Regards
Sanjeev
Karma is Dharma
08/28/2008 11:41 AM
Hi.. I am not able to give you a single line diagram, but will try to give you a picture.
we are a packaging line for Coca- cola, with mains and gensets, but never in paralell, then we have 1600A breakers and a switchgear, from here goes to a main DB that supplies everything (motors, pumps, valves. drives(380 side),etc..) and to a UPS and AVR for PLC and small signal instrumentation. As you can imagine we have a lot of inductive currents, plus the drives are profibus.
Thanks for your help
08/23/2008 1:18 AM
08/23/2008 1:32 AM
This equipment will help you match the PHASE before switching to and from genset. But I do not know if gensets can actually match the Phase of the huge generators use at dams of power plants.
Good Answers: 15
08/30/2008 6:12 AM
Hi Carlos,
I assume the failures occur when the power is cut from the supply company. If so then your problem could well be the inductive spike caused when the power fails. Also motors with high enertia loads turn into generators which can cause high voltages. If you can find out which pieces of your plant equipment are causing this then you need to add suppression to these.
If you cannot find the culprits then you can add protection to your VSDs. Use a fast blow fuse in the feed to each VSD and a varistor across the input. The varistor will clamp the voltage and blow the fuse before the voltage reaches destructive levels in the VSD. Carry a stock of these as they usually fail when protecting the circuit.
You may find that you already have this protection inside your VSDs and that with a bit of research you can get the appropriate components and have the VSDs repaired locally by a competent electronics tech.
New Zealand - Member - New Member
08/31/2008 4:36 AM
Hello Carlos57
There are two major mechanisms for input failure.
  1. Voltage transients.
  2. current surges.
It is possible that when the supply is switched over from generator to main supply, that there are voltage surges due to rotating motors and the like. These voltage surges will cause a current surge through the input rectifiers as the voltage is applied via the rectifiers to the DC Bus capacitors. The current surge can easily cause rectifier failure.
After the genset is taken off line, there can be a drop in the DC bus voltage followed by a sudden re-application of full line voltage. Once again, this can cause a current surge as the mains voltage charges the capacitors back up to the normal rail voltage.
The addition of 3% or 5% line reactors and semiconductor fuses in series with the input to each VFD will help to a) reduce the amplitude of the current surge and b) provide rectifier protection if the current gets too high.
Best regards,
Mark.
06/15/2010 7:48 AM
we suggest you to use 3 Phase AC Line chokes. This introduce additional impedace & protect drives from power problems
contact info@sve.co.in for full details
regards
Srinivas
Virgo Technologies,
India
Emeson AC drives Dealer