Problems with Danfoss Drives

08/22/2008 8:44 AM

I am in Angola in a place which have a lot of power cuts, we switch from mains to gensets and backwards, I have a lot of frequency drives blown in the 380V side, I already have a UPS and a Voltage regulator. Who can help me to solve the problem?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Problems with Danfoss Drives

08/22/2008 10:37 AM

The generator set supplier and the drive manufacturer should be at the top of the list.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#2

Re: Problems with Danfoss Drives

08/22/2008 11:00 PM

Hi.. I can help you zero-down on the root-cause of the problem. Can I have the single-line diagram of the power-flow in your facility right from Utility point to Drive.

Regards

Sanjeev

__________________
Karma is Dharma
Register to Reply
Member

Join Date: May 2008
Posts: 5
#5
In reply to #2

Re: Problems with Danfoss Drives

08/28/2008 11:41 AM

Hi.. I am not able to give you a single line diagram, but will try to give you a picture.

we are a packaging line for Coca- cola, with mains and gensets, but never in paralell, then we have 1600A breakers and a switchgear, from here goes to a main DB that supplies everything (motors, pumps, valves. drives(380 side),etc..) and to a UPS and AVR for PLC and small signal instrumentation. As you can imagine we have a lot of inductive currents, plus the drives are profibus.

Thanks for your help

Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#3

Re: Problems with Danfoss Drives

08/23/2008 1:18 AM
__________________
If you never do anything you never have problems.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#4
In reply to #3

Re: Problems with Danfoss Drives

08/23/2008 1:32 AM

This equipment will help you match the PHASE before switching to and from genset. But I do not know if gensets can actually match the Phase of the huge generators use at dams of power plants.

__________________
If you never do anything you never have problems.
Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#6

Re: Problems with Danfoss Drives

08/30/2008 6:12 AM

Hi Carlos,

I assume the failures occur when the power is cut from the supply company. If so then your problem could well be the inductive spike caused when the power fails. Also motors with high enertia loads turn into generators which can cause high voltages. If you can find out which pieces of your plant equipment are causing this then you need to add suppression to these.

If you cannot find the culprits then you can add protection to your VSDs. Use a fast blow fuse in the feed to each VSD and a varistor across the input. The varistor will clamp the voltage and blow the fuse before the voltage reaches destructive levels in the VSD. Carry a stock of these as they usually fail when protecting the circuit.

You may find that you already have this protection inside your VSDs and that with a bit of research you can get the appropriate components and have the VSDs repaired locally by a competent electronics tech.

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#7

Re: Problems with Danfoss Drives

08/31/2008 4:36 AM

Hello Carlos57

There are two major mechanisms for input failure.

  1. Voltage transients.
  2. current surges.

It is possible that when the supply is switched over from generator to main supply, that there are voltage surges due to rotating motors and the like. These voltage surges will cause a current surge through the input rectifiers as the voltage is applied via the rectifiers to the DC Bus capacitors. The current surge can easily cause rectifier failure.

After the genset is taken off line, there can be a drop in the DC bus voltage followed by a sudden re-application of full line voltage. Once again, this can cause a current surge as the mains voltage charges the capacitors back up to the normal rail voltage.

The addition of 3% or 5% line reactors and semiconductor fuses in series with the input to each VFD will help to a) reduce the amplitude of the current surge and b) provide rectifier protection if the current gets too high.

Best regards,

Mark.

Register to Reply
Anonymous Poster
#8

Re: Problems with Danfoss Drives

06/15/2010 7:48 AM

we suggest you to use 3 Phase AC Line chokes. This introduce additional impedace & protect drives from power problems

contact info@sve.co.in for full details

regards

Srinivas

Virgo Technologies,

India

Emeson AC drives Dealer

Register to Reply