Calculating Voltage Drop

08/22/2008 4:41 AM

I have a problem in one of my xlpe cable , wherin their is a voltage drop at the machine end say i have connected from distribution breaker 2 cable of 3 1/2 c 185 sqmm copper cable to a 3 phase 380v ,300 kw motor star delta , when on load the voltage drops almost to 330 V .The lengh from distribution board to motor is about 200 meters.

Please if their is any thumb rule for calculating voltage drop or table.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Voltage drop

08/22/2008 5:20 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#2

Re: Calculating Voltage Drop

08/22/2008 10:45 AM

Dear,

There is no need to use 3 and half core cables for motor feeders.

You need to change to 2 x 3 core x 300 sqmm xlpe cu cable. Assumind derating of 0.75 and ambient air temp of 40 deg C the voltage drop will be around 2.23%.

Have a standard manufacturer cable catalogue and they give you all details of the cables.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3

Re: Calculating Voltage Drop

08/22/2008 3:12 PM

I under stand that yours is 300 kw motor in star delta formation.you have indicated that 2 runs of 185 sq mm copper cable is connected.

Apparently for star delta connected motor there will be 6 connections from the starter.the full load current phase current will be 328 amps and line current will be 1.732 x 328 amps.

since two runs of cables are run, I presume one run only since it is delta connected.in this case the 185 sq.mm copper cable ,buried under ground can carry only 290 amps.

Cable size is inadequate, therefore you get very high voltage drop.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4
In reply to #3

Re: Calculating Voltage Drop

08/22/2008 6:41 PM

Quote "I under stand that yours is 300 kw motor in star delta formation.you have indicated that 2 runs of 185 sq mm copper cable is connected.

Apparently for star delta connected motor there will be 6 connections from the starter.the full load current phase current will be 328 amps and line current will be 1.732 x 328 amps."

I am not used to referring to a motor in kw, but since the post stated 300 kw at 380 volts, 300 kw/(.380 x 1.73) = 456 amps. The amps would be higher if you use KVA.

Quote "since two runs of cables are run, I presume one run only since it is delta connected.in this case the 185 sq.mm copper cable ,buried under ground can carry only 290 amps."

Why would you presume only one run when the post states 2 runs?

Quote"Cable size is inadequate, therefore you get very high voltage drop."

Not if there are 2 runs. VD is about 16 volts L-L or 364 volts.

Register to Reply
Active Contributor

Join Date: Jul 2008
Posts: 13
#6
In reply to #4

Re: Calculating Voltage Drop

08/23/2008 10:13 AM

It is 2 runs of cable running from main distribution panel with a distance of 150 meters connected to a control panel breaker with a motor load say 250 KW which is star delta connected with 6 terminals. when motor is on full load around 446 amps, the voltage drops on the mains of control panel . Please clarify and request for suggestion.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#8
In reply to #4

Re: Calculating Voltage Drop

08/24/2008 3:34 AM

"I am not used to referring to a motor in kw, but since the post stated 300 kw at 380 volts, 300 kw/(.380 x 1.73) = 456 amps. The amps would be higher if you use KVA."

I am sorry to intervene, you have not considered the power factor,when the motor is rated for 300 kW,you have to take pf into conideration for calculating the ful load current.

Therefore the full load line current would be I=(power)/(pf*line voltage *1.732).

in this instance, I=(300*1000)/(1.732*0.8*380)=569.7 Amps.

The phase current would be=328 amps.

From the recent post by the member I understand there is a main panel from which the starter is fed by two runs of 185 sq.mm copper cable.From the starter panel to motor there should be cable which should have 6 core ( 2 x 3 core).(delta formation)

The current flow on the cable between main panel to starter panel would be 569.7 amps and the current flow on the cable between starter and the motor will be 328 amps.

The cable should be designed for the above current rating.

The member has not indicated the cable particulars between the starter and the motor , therefore I have to assume the cable as single run.

Voltage drop can be arrived at if proper and all information are made available.

The voltage drop indicated by the member is very high but it should not be attributed only to cable.

There are 6 terminations in the route from the main panel to motor.

Even if the terminations are bad or contacts are bad the voltage drop will be high.

One has to visit the site and examine the installation.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9
In reply to #8

Re: Calculating Voltage Drop

08/24/2008 5:34 PM

Ramvinod

Thanks for your comments. In the original post the writer said

Quote" i have connected from distribution breaker 2 cable of 3 1/2 c 185 sqmm copper cable to a 3 phase 380v ,300 kw motor star delta ". I took that to mean he had a star distribution panel but he was connecting the motor as a delta. I did not think he was referring to a star - delta starter. I agree that the PF should be included in the calculations and I made that point in my first post. Thanks for your added information.

Register to Reply
Anonymous Poster
#5

Re: Calculating Voltage Drop

08/23/2008 8:45 AM

DEAR FRIEND YOU USE THE FOLLOWING FORMULA FOR 3PH.POWER LOSSES.

= 3xCosΦxLxRxT ⁄ 1000.

:CosΦ is what you maintain your P.F

L = Length, R = Resistance of cable , T = Temperature

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#7
In reply to #5

Re: Calculating Voltage Drop

08/23/2008 8:45 PM

Quote "

DEAR FRIEND YOU USE THE FOLLOWING FORMULA FOR 3PH.POWER LOSSES.

= 3xCosΦxLxRxT ⁄ 1000."

That is not correct. If you are referring to line losses in watts it is

I² x resistance of the conductor. If you are speaking of voltage drop, the formula

is VD = IR(cosΦ)+ IX(sinΦ) where R is the resistance and X is the reactance of the conductor. I = KVA/ Z x 1.73 where Z is the impedance of the system. You are using KW and Resistance which will not give you the correct answer. IF you are referring to the motor in KW, the actual amps will be less than when you use KVA which is the actual load.

Register to Reply
Participant

Join Date: Oct 2008
Posts: 1
#10

Re: Calculating Voltage Drop

10/15/2008 8:27 PM

Kumar, I presume 380/3/50/579A load serviced by (2) 3½ c 185mm2 Cu XLPE in ferrous raceway

Voltage Drop... by circular mil (CM) method applied to metric cable »

k = Rdc for 1000 CM conductor 1000ft long say copper = 12.9 CM-ohm/ft [ft/.3048M] ~ 42.32 CM-ohm/M

Q = inductance adjustment factor [Rac/Rdc] applied to conductors greater than 50mm2

VD% = SQRT(3) * k * Q * I * D / E / CM

SQRT (3) * [42.32] * 1.196 *570A * 200M / 380v / 730,216 CM ~ 3.6% voltage drop

Register to Reply
Register to Reply 10 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); greanurth (1); jsuresh kumar (1); PWSlack (1); ramvinod (2); wareagle (3)

Previous in Forum: Wiring Batteries in Series   Next in Forum: Problems with Danfoss Drives
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement