In a NATO base in Afghanisthan, there were 6 x 1 MW Disel Generators installed for their Garrison out of which the Power Plant engineer was operating 2 Generators each at 60% load. When the writer checked the records and operating conditions, noticed that the load is only 80% maximum for one set and such advised to take the entire load on one set and switch off the 2nd operating Generator. Within 6 hrs of such change over, suddenly the Local control MCB of the generator tripped and there was power interruption for over 25 minits even though the Black Start Generator was on line within in 20 minutes of tripping of the MCB. The operator entered the generator room after opening the door with much difficulty as it was under negative pressure since the generator has not yet stopped and the black start also runing. As no power was available, the roof mounted fresh air fans for Radiators were not on. The generator room was stinking like hell with foul smells coming through the floor drains as the fresh air is being sucked for radiators thro them. No floor trap could be provided on them due to sub zero temperature freezing the trap water. Operator manually stoped the runing generator as well its 15KV breaker and in 7 seconds, the standby generator came on line restoring the power supply. On investigations, it was noticed that not only there was no audio/visual anounciation of the fault but even the stand by generator did not start within 11 to 13 seconds which caused the black start to come one line. It was also observed that the local control MCB which has been mounted on the Generator frame has tripped. The solid copper bus bars connecting the alternator to Local control MCB was dis coloured and v hot even though the load was 80% only.The MCB has tripped due to the vibration of the Generator as well as the heat contributed by the over heated bus bars. A push off microswitch was installed at the foot of MCB cam and wired in series with the tripping coil of 15KV breaker. It was observed that the mechanical tripping signal came when again the same fault occured, the relevent 15KV breaker went on off Mod and not in lock out mod making istanious starting of the standby Generator and avoiding the Black start coming on. Now the question is: (1) That the bus bar is under size or not? (2) The Alternator should have been connected to MCB with cable instead of sold copper bus bar to avoid transmission of vibratin or not? (3) The MCB should have been on an inependent pedestal completely seperated from the Generator base frame or nor? (4) Is the above are a design/manufacuring fault on the part of OEM or not?