Hello Frnds,
We are having a pressurised feed (Crude Oil) tank with design pressure of 10"WC TO -2 "Wc with safety valve mounted on top of it with set value of 8 " WC & -1 " WC
I want to know how PZV will Work/Logic on the negative side.
Regards
Jose
Re: Safety Valve Setting
08/26/2008 4:21 AM
It can be expected to operate at -1"wc if correctly installed and maintained.
1"wc is well within the normal swings of barometric pressure due to local weather conditions.
08/26/2008 7:50 AM
Dear Frnds,
Thanks for Inputs ,As mentioned in the link , We are having same application tank is being pressurised with Fuel gas .
I guess In PID PZV should Be PV
Regards
Jose
08/27/2008 11:23 AM
just a little curious,doesn't the valve sales company or manufacturer advise on techical information.
08/27/2008 1:28 PM
The tank is designed for 10"WC and the set pressure is 8" WC.
If this is a pallet loaded type relief valve it takes 100% over pressure before the valve lifts full.
Unless the valve is grossly oversized the valve may not reach the full capacity required if this is weigh loaded device
If you don't know where you are going,you are bound to get there