Insulation testing of a 6.6 kV Generator

08/26/2008 10:53 PM

Dear Sir,

We have a 6.6 kV Synchronise generator (1500 kVA) in our mini hydro power plant. Here I want to test its insulation, what could be the method I can follow for this?

Including testing Voltage should be used for insulation testing to evaluate the insulation level of the generator.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Insulation testing of a 6.6 kV Generator

08/27/2008 3:24 AM

Follow the original equipment manufacturer's maintenance instructions, which will be found in their User Manual.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#2

Re: Insulation testing of a 6.6 kV Generator

08/28/2008 12:00 AM

Like he said follow the instructions then test it at the systems breaker box or load dump.

__________________
If you never do anything you never have problems.
Register to Reply
Anonymous Poster
#3

Re: Insulation testing of a 6.6 kV Generator

08/28/2008 8:59 AM

You mean 6.6 kW? If so, and you have 1500 kVA, the you are producing 230 Volts with the generator. The max leak-current is then calculated 230*1000 = 0,23MOhm.

You need to shut down the system, disconnect the generator and measure the insulation with an insulation meter (Megger), addjust the megger to 500V and test the phases to ground.

Regards

Mundi

Register to Reply Score 1 for Off Topic
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#4
In reply to #3

Re: Insulation testing of a 6.6 kV Generator

08/28/2008 9:09 AM

WHAT???

__________________
Never trade luck for skill.
Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#5
In reply to #3

Re: Insulation testing of a 6.6 kV Generator

08/28/2008 10:45 AM

Hello Sir ,

Selecting the megger voltage range is based on which parameter ? , Please .

Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#6

Re: Insulation testing of a 6.6 kV Generator

08/28/2008 2:00 PM

Below is a chart with test voltage levels for different system voltages. 2500VDC is standard for medium voltage generators. If the machine is a wye configuration you will need to lift the neutral from the ground bus or resistor.

Be extremely careful, as depending on your system configuration it is possible to have more than one generator sharing neutral connection..

Insulation Resistance Test Values
Electrical Apparatus and Systems

Nominal Rating
of Equipment in Volts

Minimum Test Voltage, DC

Recommended Minimum
Insulation Resistance in
Megohms

250 500 25
600 1,000 100
1,000 1,000 100
2,500 1,000 500
5,000 2,500 1,000
8,000 2,500 2,000
15,000 2,500 5,000
25,000 5,000 20,000
35,000 15,000 100,000
46,000 15,000 100,000
69,000 and above 15,000 100,000
Register to Reply
Commentator

Join Date: Aug 2008
Posts: 82
#7
In reply to #6

Re: Insulation testing of a 6.6 kV Generator

08/29/2008 9:53 AM

Will this Equip. voltage rating is irrelevant with Applied freq.rate ?

For transformers : references , please . Thanking you , Sir .

Register to Reply
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#8
In reply to #7

Re: Insulation testing of a 6.6 kV Generator

08/29/2008 10:17 AM

yes, these ranges will work for transformers as well..

Frequency of power system does not matter as you are using DC test voltage with megger.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2008
Posts: 82
#9
In reply to #8

Re: Insulation testing of a 6.6 kV Generator

08/29/2008 10:20 AM

Thanks for all your Assistances , Thanks .

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dadw5boys (1); ekiechle (2); PWSlack (1); sivaa (3); wangito (1)