RTD temperature probes

08/27/2008 11:00 AM

I have some faulty 3 wire ? resistance temperature probes with the following coloured wires on them Red, white and blue, I assumed them to be 4 wire units with the two blue wires connected to make a 3 wire. As they are all open circuit I cannot determine what type of RTD they should be to obtain replacements- any ideas.

The equipment range is 50 to 250C

__________________
A day without a smile is a day lost
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: RTD temperature probes

08/27/2008 11:31 AM

Say the wires are 1, 2, 3 and 4.

Select a multimeter, set to low ohms value.

Measure between wire 1 & 2, 1 & 3, 1 &4, 2 & 3, 2 &4, 3 & 4.

There should be four readings in excess of 100Ω and two readings of anywhere between 0Ω and 1Ω.

Which means that 2 of the wires are connected to one end of the resistance, and two to the other.

Now the 4-wire device can be wired to a 3-wire set of terminals correctly, by leaving one lead of the 4-wire device disconnected, and the measurements show which one it can be.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 11
#2

Re: RTD temperature probes

08/27/2008 11:49 AM

U can go for a normal 3 wire RTD. there should be no problem.but take care about the compensation.

Register to Reply
Anonymous Poster
#3

Re: RTD temperature probes

08/28/2008 4:42 AM

RTDs are usually 3 terminal device. two of which are shorted at the probe for us to calculate the wire resistance of your cable used, so that the 3 wires should be identical and same length to have identical resistance, to get the temperature you should get the resistance of the 2wires and thermistor, then subtract the resistance of the shorted wires. but since the wires are open, you should contact the manufacturer and give the serial number of the device so that they can assist you.

Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#4
In reply to #3

Re: RTD temperature probes

08/28/2008 4:46 AM

Thank you guest.

The problem is that there are no manufacturers marks and all wires are open circuit.

__________________
A day without a smile is a day lost
Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 11
#5
In reply to #4

Re: RTD temperature probes

08/28/2008 7:45 AM

Four-wire RTD's provide slightly better compensation, but are generally found only in laboratory equipment and other areas where high accuracy is required. When used in conjunction with a 3-wire instrument, a 4-wire RTD will not provide any better accuracy. If the fourth wire is not connected, the device is only as good as the 3-wire RTD; if the fourth wire is connected, new errors will be introduced. Connecting a 3-wire RTD to a 4-wire instrument can cause serious errors or simply not work at all, depending on the instrument circuitry. A 2-wire RTD can be used with either a 3 or a 4 -wire instrument by jumping the appropriate terminals, although this defeats the purpose and reintroduces the un compensated resistance of the leads

Register to Reply
Power-User

Join Date: Dec 2005
Location: Willenhall, UK
Posts: 159
#6
In reply to #5

Re: RTD temperature probes

08/28/2008 7:50 AM

I wondered if the red,white, blue colour code signified that they were PT100 or N1000 or somme other range?

__________________
A day without a smile is a day lost
Register to Reply
Guru

Join Date: Jun 2007
Posts: 1035
Good Answers: 40
#7
In reply to #6

Re: RTD temperature probes

08/28/2008 9:24 AM

From the For-What-It's-Worth department ... got a scanner?

You might hit the jackpot (as I did once) sending a good picture, with a 6" SS pocket rule or other size-reference therein, to a couple of good Source-Contacts. Of course, include ALL available design/operating parameters with the email...

Wishing you success ~

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#8

Re: RTD temperature probes

08/28/2008 12:04 PM

You should be able to figure it out from the instrument end. If you have a decade resistance box it's dead simple. Connect the decade box in place of the RTD, then adjust the resistance until you get a reading of 0°C on the instrument. Then compare the resistance value on the decade box with an RTD standard chart to determine the type of sensor. In some cases, there are 2 or more standard RTD's with the same reference point (for example, there are 2 standard Pt RTD's with 100Ω @ 0°C. In that case you'll need to get temperature readings at 2 different resistance values determine the temperature coefficient of resistivity.

If you can't get a decade box, you can use various fixed resistors (10, 100, 120, 200, 1000Ω) instead.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2007
Location: Gdansk, Poland
Posts: 100
Good Answers: 2
#9

Re: RTD temperature probes

02/04/2009 9:48 AM

Try to find RdF(RTD-s maker) web page. But firms do not have the same color codings. So probably last suggestion (using resistance box to identify RTD) is best solution.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); czgut (1); martin (2); ndt-tom (1); peterd (2); pwr2thepeople (1); PWSlack (1)