Can I run two 230 volt hand dryers using one 230 volt 3 phase tap. Each dryer is rated at 9.1 amps tap is rated at 25 amps. Rick Webb

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#1

Re: Rick Webb Dairy Farmer

08/31/2008 4:22 PM

Follow code for wherever you are. 230V 3 phase, where are you?

Tap?--Transformer tap?

Wire and size your fuses or breaker for 25A off the secondary or the tap--Is the Primary protected properly if this a transformer? AWG 10 is good for 30A, but don't exceed 25A on the fuse or breaker.

Air movers tend to run real close to their full load amp ratings, so I would count on the 9.1A. I would wire them so that they start independent of each other. The high inrush current of both may give you a tripping problem if they start simultaneously.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Participant

Join Date: Aug 2008
Posts: 1
#2
In reply to #1

Re: Rick Webb Dairy Farmer

09/01/2008 9:43 AM

The tap I am refering to is a power bar where 230 volt 3 phase is present then you insert the fuse /taps into to facilitate getting power. R.W.

Reply