09/03/2008 6:25 AM
I'm posting this in the Chemical & Material Science group instead of Electrical Engineering because, though involving electrical resistance, it is just as much a material issue (the water), and I've already made a few friends here who have been very helpful, and I thank them again. I've been shopping around for steam boilers and came across this statement:
"NOTE: Water with a minimum of 1 meg ohm-cm specific resistivity must be used for proper & safe boiler operation."
I'm trying to learn what that means for sure, although I think I _might_ have a _rough_ idea. I know that an 'ohm' is a measure of electrical resistance, and it seems to me that the statement is saying that if I put some water in a beaker and use a meter with probes 1 cm apart, that I need to measure at least 1 million ohms of resistance. I know that pure water without any mineral content can not conduct electricity, and we have already been planning to use reverse osmosis water in our boiler for two reasons: first, besides just steam, hot water from the boiler will go into the beer we'll be making, and we want distilled-quality water so that we can add our own minerals to reach the different water profiles we will want for different styles of beer; and second, we don't want minerals to collect in the boiler from our generation of a lot of steam, and then have down-time cleaning scale or other problems. So I guess the questions I really have are:
1. Is my understanding above correct?
2. Any idea if RO water would likely meet that requirement, because I've never read anything like that on any spec sheets for RO filters?
3. Any other thoughts or comments?
Thanks in advance.
Bill Velek
My personal non-profit project to help humanity - http://www.2plus2is4.com - 'Why our schools should teach our children about grid-computing'
Pathfinder Tags: water resistivity
Good Answers: 143
Re: What does "1 meg ohm-cm specific resistivity" mean?
09/03/2008 6:43 AM
The electrical relationship that you are looking for is
ρ = RA/l
where you measure the resistance of a sample (let's say a column of water 1 cm X 1 cm (A = 1 cm2) and 10 cm long. If you measure 10,000,000 Ω, you have
ρ (the resistivity) = (107Ω)(1 cm2)/10 cm = 106 Ω cm
04/17/2009 3:09 PM
not wat i was looking for and it made no sense!!! i had to think hard... THANKS ALOT!!!
NOT USE FULL!!!!!!!!!!!!!!!!
09/03/2008 7:03 AM
What the boiler manufacturer is trying to do is two things:
  1. Preserve its reputation
  2. Give the customer guidance on the sort of feed water that will preserve that reputation.
OK. Boiler water treatment using RO in a nutshell <takes a deep breath>.
Boilers, and cooling towers incidentally, do the same thing - they evaporate water, leaving the dissolved solids behind. Eventually the dissolved solids build up to the point where economic operation is not possible, at which point some of the water must be blown down and made up with fresh feed. Blowdown also removes some of the settleable solids that also accumulate.
Low pressure boilers will operate on virtually any feed water except sea water - for a while. The cleaner the feed water, the longer the boiler will run between blowdowns.
That's not the whole story. In order for the boiler to operate in the long term with minimal mechanical replacment, the water must be maintained slightly alkaline, usually by dosing something like caustic soda in small quantities.
Resistivity in MΩ.cm is the reciprocal of conductivity in μS/cm. It is used as a measure of how little dissolved substances are present in any water. Locally, the drinking water is around 750μS/cm and well up in calcium - a slight taste though good enough to drink and very wholesome. It would be a problem for a boiler with a maximum recommended drum conductivity of 3000μS/cm as it would have a concentration factor of 4 before blowdown were needed. A well-balanced RO plant might take that feedwater down to, say, 3-4μS/cm in one pass, with next to no calcium and a terrible taste. The dissolved solids from an RO come out in the reject stream. A second pass might be needed to get to this manufacturer's boiler water quality target. At a feed level of 1μS/cm, the concentration factor is now 3000, so this is why the economics of operation are important - it is cheaper to demineralise the feed than to operate the boiler at high blowdown levels. In this example, the blowdown frequency is 1/750 of that when operated on town mains feed water, and energy and treatment chemicals will be saved by these sort of figures too. This is what the boiler supplier is keen to do as well, as the reputation improves with the cleanliness of the feedwater.
The instrument used to measure water purity is known as either a conductivity meter or a resistivity meter, depending upon the purity of the water being measured. It's basically an AC current being passed between two electrodes in the stream. By knowing the shape and separation of the electrodes, the current flowing and the temperature, the conductivity/resistivity of the stream can be calculated within the instrument and presented for display and use.
It is incorrect to describe an RO plant as a filter. It doesn't block in the way that a filter does. However, depending on the incoming local water quality, additives might be required in the feed to maintain an RO plant in non-fouled condition; as the concentrate gets to the back of the elements the levels of bivalent and trivalent species can start to rise to precipitable levels. The most common additive is sodium hexametaphosphate, which acts by 'complexing' the precipitables so that they remain dissolved and pass out with the reject stream.
Additives are usually required on seawater, and might not be required if a good clean borehole or river source were available, though the answer depends upon local conditions. Oh, and a seawater plant contains different membranes than a towns water plant, as the osmotic pressure of seawater is much higher. From an incoming conductivity of, say, 50,000μS/cm, a typical outlet conductivity of a seawater-to-towns-water plant might be in the order of 100-200μS/cm - drinkable after "re-hardening", though not good enough for the boiler in question. The second pass would go through different membranes to produce 'technical water' for this particular boiler, without re-hardening.
So the course of action w.r.t. this boiler is to match the manufacturer's feedwater requirements with the local water sources via a feedwater treatment plant of some sort. There are many reputable specialists in this field and a Google search locally will doubtless provide a number of telephone contacts that could be approached for further advice and an outline proposal for a package plant that would do the job. Go talk to them!
Will that do for now?
09/03/2008 10:40 AM
PWSlack wrote:
snip
Thanks. I presume that the boiler manufacturer would be able to address
that, such as the exact quantity/concentration.
snip
Yes. I rated this as a 'GOOD ANSWER'; not only have you confirmed my
initial impression, but you've provided some good additional info, too.
Thank you VERY much. I do have a brief follow-up, if you don't mind.
When you mentioned "dosing something like caustic soda in small
quantities", I presume that ... if this boiler were to be used
exclusively for steam ... that there would merely be an initial dosing
and that the caustic should remain in the boiler since it wouldn't be
contained in the steam (perhaps the manufacturer even does that prior to
shipping). However, most of the water from the boiler we will be using
will actually exit as hot water rather than as steam, which would carry
the caustic with it, although much of it will also exit as steam for
various uses during the brewing process. Is it a fair guess to expect
that, despite any steam usage, we should still be able to maintain the
proper level of caustic in solution by monitoring the concentration in
the water leaving the boiler, and that the levels should not build up to
a level that would eventually require a blow-down?
Thanks in advance.
Bill Velek
09/04/2008 7:51 AM
<...caustic soda in small quantities......the boiler manufacturer would be able to address that, such as the exact quantity/concentration...>
Nope. Contact a specialised boiler feedwater treatment chemicals specialist. Nalco (usual disclaimer) springs to mind as a chemicals supplier, and Prominent (usual disclaimer) as a dosing equipment supplier. These and others all have a web presence.
<...there would merely be an initial dosing and that the caustic should remain in the boiler since it wouldn't be contained in the steam...>
Nope. The caustic will react with certain species in the boiler, and any residual will be lost from the system during blowdown, and will need to be replenished. A boiler water treatment chemicals specialist will be able to advise and supply the necessary.
<...the levels should not build up to a level that would eventually require a blow-down...>
Blowdown is always required (both in boilers and in cooling towers), as the remaining dissolved substances in the feedwater, as well as the dosed caustic, will concentrate-up as steam/vapour is drawn off. The interval between blowdowns will be determined largely by the concentration ratio as suggested in the earlier post. It is common to blow a boiler down at, say, 3000-6000μS/cm, and to omit this operation will result in the boiler priming, eventuallk; priming is when water droplets get carried over into the steam system - the boiler starts to 'froth'.
The cleaner the feedwater in terms of the absence of dissolved substances, which is indicated by a high resistivity/low conductivity, the less frequent the blowdown operations will be, and the better the economics.
09/04/2008 12:31 PM
PWSlack wrote:
snip
snip
Thank you for taking the time to respond and explain this science to me; I am most grateful for your help and so I don't mean to offend you in any way whatsoever, but please let me get some clarification.
I'm still having difficulty understanding why a blowdown would _EVER_ be required in _MY_ situation, considering that regular "water heaters" are _never_ blown down ... or at least I've never heard of it ever being necessary before ... so I think I've probably just failed to make myself clear.
First, we will be using R/O water, so the mineral content will be _substantially_ below precipitation levels for any and all minerals.
Second, the relatively small amount of steam that we will draw from the boiler (probably not ever more than 15% of the water we add) ... should not leave behind enough minerals to elevate levels in the remaining water to anywhere even remotely close to precipitation levels; e.g., if R/O cut calcium to 5% of what was dissolved in municipal water, and I boil away HALF of the water as steam, I would still only have a concentration of 10% of what was dissolved in the municipal water, so wouldn't it all remain in solution in the hot water?
Third, the rest of the water will be drawn off and used as hot water, which should carry the dissolved minerals with it, and therefore, I would suspect, have the exact same effect as a blowdown -- the minerals are removed from the boiler.
To give you something specific, for a typical 1.5 barrel batch of beer, we will use 56.5 gallons of _water_ and then use steam generated from about 6 gallons of water. In addition, we will use a fairly nominal amount of steam to purge and clean our lines, and some to steam-clean our fermenters, tanks, and any kegs (since we plan to 'can' most of our beer, kegs should comprise a fairly low percentage of our production). I don't know for certain how much steam will be used for the cleaning, but I can't imagine that it would use more than a couple of gallons of water. So I think a good estimate is that the ratio will probably be about 56.5 gallons as water : 8 gallons as steam -- so about 12.4% of the water will be converted to steam, and the rest drained as hot water. If, in such a situation, a blown down and/or addition of a bit of caustic soda is still required, please let me know.
Thanks.
Bill Velek
05/23/2023 3:52 AM
<...difficulty understanding why a blowdown would _EVER_ be required...>
Because it's a separation process. The dissolved substances in the feedwater remain in the boiler drum and do not leave with the steam stream; they concentrate-up over time. Species such as calcium sulphate ("gypsum"), calcium carbonate ("limestone") and magnesium carbonate ("marble") are things that are not wanted in the boiler drum as their solubility decreases with rising temperature. "Kettle scale". The tendency is for these to precipitate-out onto heat exchange surfaces, adding insulation to them in the water space, reducing the thermal efficiency of the unit, and thereby making the combustion-side of the wall run hotter, leading to creep, fatigue and eventually material failure. Further, these things increase the tendency of the boiler to "prime", i.e. carry-over water into the steam stream, with rising concentrations of dissolved substances. This is why regular blowdown is necessary and periodic washout is a valuable planned preventative maintenance [PPM] procedure.
Reducing the concentrations of dissolved substances in a boiler feedwater, often with reverse osmosis equipment among other things, is therefore a Good Thing.
<..."water heaters" are _never_ blown down...>
This would be due to there being no separation process taking place within them. Cold water in. Hot water out. The End.
Periodic washout of <...water heaters...> as a PPM will still be found valuable.
09/03/2008 12:11 PM
I prefer the term micro-mhos for conductivity.
I mean, it's brilliant - take the reciprocal of resistance (ohm) and spell the word backwards (mho). I get a chuckle every time I here that unit: µmho ....
(sorry I could resist commenting, plus I am bored at work.)
09/05/2008 4:59 PM
Dear Sir!
The latest unit for conductivity is Siemens denoted by "S"
Please see any of the Multimeters by Fluke having conductivity measuring facillity.
Regards
Re: What Does "1 Meg Ohm-cm Specific Resistivity" Mean?
09/04/2008 10:19 AM
Frame of reference:
18 megohm water is very highly purified, devoid of any substance but H20, ultrapure water used in the electronics industry for chip manufacture, for example.
10 megohm water is highly purified with typically an ion exchange demineralization process (could be reverse osmosis/demin, electrodeionazation, or similar) that is a typical goal for high pressure boiler operation such as in utility central stations.
09/04/2008 10:58 AM
The answers so far have answered the question. However, please do not add caustic soda to the feed water in a high pressure boiler. Usually a boiler that calls for meg ohm water is a high pressure boiler, 1000 to 1750 psig operating pressure, and adding caustic soda to the feed water will cause a boiler failure, and it may be fail before leak. Contact your local feed water treatment specialist such as Nalco or Calgon and get a good coordinated treatment program.
09/04/2008 1:55 PM
harralrw wrote:
> snip ... please do not add caustic soda to the feed water in a high
Thanks. I just happened to come across that statement about resistivity while I was searching for a potential boiler, and didn't know what it meant or when it applied; it no doubt was not with the same information.
The largest unit that we are considering (or something similar) is the "Reimer's Electra Steam" model "HL-265" which has the following specs:
BTUH Out Put: 895,000
KW: 265
Water Capacity: 71 gallons
Maximum temperature is 240F, which I believe creates about 10 p.s.i. ... which I'm sure is considered a low pressure system. But THANKS for the safety warning.
Cheers.
Bill Velek
09/04/2008 11:05 AM
"...go into the beer we'll be making..."
Right! All very helpful, I'm sure, all very critical information to have. Now, about that beer...
09/04/2008 12:06 PM
If you are lucky enough to have good feed water you may be able to use polishing filters instead of Reverse osmosis. They are a lot cheaper.
Really pure water is a great solvent for almost everything. You can get your water too pure for some types of pipe.
09/04/2008 2:17 PM
Thanks for the advice. I'll get the specs for our municipal water and do some research. Saving money is always good for business.
Cheers.
Bill Velek
09/04/2008 2:34 PM
"Saving money is always good for business."
Yer dern tootin' buckaroo! So's advertising - and I'm still interested in hearing about that beer... Did I move away from Rogers too soon?
09/05/2008 1:00 PM
We're not even started yet, and we'll probably never become big enough to market all the way to Florida, but if you even come back to Rogers and pass through Conway, I'm very confident that you'll hear about us then. I'm going to make a bold prediction that if we can get set up like I want, that we will max out at the 15,000 barrel per year legal limit within five years.
Cheers.
Bill Velek
09/05/2008 1:29 PM
DO keep me posted? I've actually named beers for a couple of microbreweries based on flavor and color of the product. One in Sioux Falls, SD (Brickhouse Brewery), and one in Ft. Collins, CO (O'Dells). I'm a BIG fan of regional brewing products!
09/04/2008 2:37 PM
Sorry, but "polishing filters" and "reverse osmosis" is comparing apples and oranges. In fact, it is likely that the reverse osmosis plant that you are considering will itself require "polishing filters" as one form of pretreatment prior to pumping through the RO membranes. You may require additional treatment steps.
Filters remove particulate matter that could foul the RO membranes. They do not reduce the saline content of the feedwater.
The RO system will take out well over 90 % of the dissolved solids content of your feedwater. This will likely not enable reaching your 1 Megohm target unless you have unusually low dissolved mineral content in you water supply (not likely).
09/05/2008 8:53 PM
1 megaΩ/cm resistivity is the boiler specification of the minimum quality of water purity. 18 megaΩ/cm resistivity is a much more purify water, it is often use in electronic industry. The water at 1 megaΩ/cm resistivity is highly corrosive, stainless steel piping or PVC.... should be used instead of regular copper pipe.
If you are commercial brewery, you should contact your local water treatment company to install a water treatment system, it is best to leave it to the specialist so you can concentrate on your field.
If you are an hobbyist like I am, you may try my set up (I made my own beer and wine) as following:
incoming water - catalytic conditioner - Sediment tank with up ward charcoal filter - RO - boiler (in my case a converted pressure cooker)