star-delta or DOL

09/17/2008 1:08 PM

Dear friends,

self worked in a refinery (jamnagar-india) as an electrical engineer and commissioned more than 100 motors. But i have never come across a motor with star-delta starter.

Now i am working in an automobile plant (pune-india), the first motor that i commissioned had a star-delta starter.

My question is:

is there any particular reason why star-delta starters are not used in refineries?

Pls clarify

Regards

Prashanth

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#1

Re: star-delta or DOL

09/17/2008 11:20 PM

Maybe Ambani's Consultant wrote a 1-line spec. "All DOL". Huge Power system--OK-- every application will start-maybe 6 times inrush current.

Also avoided human errors---when to switch over to Delta. Also minimised maintenance of sparking brushes. And enabled easy/Cheap remote auto start/stop/start on computer control.

Pune-- Small scale -- limited power connection.

Maybe the machine starts on no load.

So preferred S-D

MM

Register to Reply
Associate

Join Date: Jul 2008
Posts: 37
#2

Re: star-delta or DOL

09/17/2008 11:29 PM

hi

star delta starter is basically used to smoth start of the motor such that the starting of the motor do not affect the other runnig equipements of the same bus, where in motor will initially run as lower voltage i.e. 415/1.73 and then switch over to 415 v.

in this starter when motor initally run with star connection, it run with slower speed and torque to output LPM and pressure of the fluid will be also less after putting in delta motor will run with full speed and torque and supply fluid with pressure, now in refinary it is required that as soon as we switch the motor ON, fluid mush provide with its rated pressure in further prosesses, so always DOL is used in such kind of requirements,

best regards

divyesh patel

Register to Reply
Active Contributor

Join Date: Jul 2007
Location: Toronto
Posts: 14
#3

Re: star-delta or DOL

09/18/2008 12:13 AM

Safety Hazard is a main concern in the selection of DOL in refinery. In star/delta, there are many chances of small spark which may burn whole refinery. Have you heard of fire incident in Delhi bring spec of FRLS into Cables?

Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#4
In reply to #3

Re: star-delta or DOL

09/18/2008 1:25 AM

In oil industry the spark and fire hazard is the main concern second as mentioned by other gentleman the inrush current and voltage dip when several motors are operating on the same bus in a process industry will play a dirty game when you start a large motor on Star delta starter available and used for general application.in fact the electrical generators for oil industry are ordered with Air start motors instead of Electrical start motors and special silencer fitted with Spark arresters are installed to take of Fire hazard.

crm

__________________
Run silent run deep
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: star-delta or DOL

09/18/2008 5:33 AM

In large plants having their own substations of 33KV and above with larger power of the order of 10MVA+ normally all motors are on DOL as the motor starting will not cause any system disturbance or voltage drops that can cause other running motors to pull out and cause certain equipments sensitive to voltage to malfunction.This plant supply may be insufficient and hence star Delta is used.Normally in all paper , cement,Refineries dol is used.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#6
In reply to #5

Re: star-delta or DOL

11/28/2008 2:17 AM