I just want to make sure,
i am reviewing datasheet, and i see statement transformer 6.6KV/240-120.
is it correct that the transformer is delta/delta ? because many system in my country use delta/wye like 20KV/380 Volt.
its mean, in secondary
phase to neutral = 220 volt.
phase to phase = 380 volt.
i see in 6.6KV/240-120 datasheet, 120 volt is exactly 240/2. this voltage only happan in delta.
because 240/v3 is 138.564 volt.
tx
Good Answers: 38
Re: transformer 6.6KV/240-120
09/23/2008 10:48 PM
Uhm, i think your mixing generators and motor terminology in there,
A transformer just has 2 coils and depending on the configuration of the second coil the output will be 240 or 120Volt, i suspect the watts will be different depending on what configuration you will use
Good Answers: 140
09/24/2008 7:56 AM
Sounds like your data sheet indicates a single phase transformer. The secondary side sounds like a center tapped 240 volt single phase winding, giving you in essence two 120 volt windings in series.
09/24/2008 10:22 AM
Sounds like you have the wrong transformer.
Re: Transformers - 6.6KV/240-120
09/25/2008 11:41 AM
Elect-OK,
We have many transfromers 6.6KV/240-120.
Primary side is delta, the transformer is really a 6900V transformer whixch can be used in star on a 12KV distribution line.
The secondary is 240 center tapped to give 120V.
Small factories and commercial building will use secondary in start to give 240 between phase and neutral and 415 v between phases.
Some distribution pole monted transformer banks do used seconday in delta to give 240 between phases and 120 V between two phases ( red and yellow) and neutral.
The blue phasee to neutral is 200V.
380V is an european power supply.