MCB Minimum Capacity

09/25/2008 6:43 AM

we are using 60 amps three phase variable transformer .input voltage is 415V and output varry from zero to 460volt.We want to know what is the minimum capacity of MCB is required.

__________________
tomy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: capacity of MCB

09/25/2008 7:14 AM

Hello tomy@sabtron.com

Please advise which MCB you need advice for:

  1. Primary MCB
  2. Secondary MCB
  3. Both MCB's

Reply here, with

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Member

Join Date: Aug 2008
Location: INDIA,KARNATAKA,BANGALORE-560030
Posts: 8
#2
In reply to #1

Re: capacity of MCB

09/26/2008 1:21 AM
Dear sir, we need both primery and secondary MCB
__________________
tomy
Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#3

Re: MCB Minimum Capacity

09/28/2008 9:23 AM

Hi tomy,

A 100A / 600V MCB would be adequate if the expected load is resistive, use at least a 200A / 600V MCCB otherwise.

regards

Register to Reply
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#4

Re: MCB Minimum Capacity

09/28/2008 8:36 PM

Hello again, tomy@sabtron.com

As per feridun above.

If you need Fault Discrimination in your arrangement, use a larger MCCB for the Primary, with a lower Amperage MCCB for the secondary.

Example: Primary: 100 AMP MCCB with Secondary 80 amp MCCB.

If magnetising current (Switch-on surge) trips either of the above MCCB's, then use: 160 Amp MCCB Primary, with 100 Amp MCCB secondary.

The use of a larger MCCB for the Primary, will ensure by (Discrimination against Cascade Fault), that if the secondary loading is too great, the Secondary MCCB will trip, leaving the Primary MCCB not tripped.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Member

Join Date: Aug 2008
Location: INDIA,KARNATAKA,BANGALORE-560030
Posts: 8
#5
In reply to #4

Re: MCB Minimum Capacity

09/28/2008 11:53 PM

thank you very much

__________________
tomy